(7) Low-Voltage Gas-Fired Luminaires, Decorative Fireplaces,
Fire Pits, and Similar Equipment. Listed low-voltage gas-fi red-
luminaires, decorative fi replaces, fi re pits, and similar equip‐
ment using low-voltage ignitors that do not require grounding,
and are supplied by listed transformers or power supplies that
comply with 680.23(A)(2) with outputs that do not exceed the
low-voltage contact limit shall be permitted to be located less
than 1.5 m (5 ft) from the inside walls of the pool. Metallic
equipment shall be bonded in accordance with the require‐
ments in 680.26(B). Transformers or power supplies supplying
this type of equipment shall be installed in accordance with the
requirements in 680.24. Metallic gas piping shall be bonded in
accordance with the requirements in 250.104(B) and
680.26(B)(7).