    Good morning,
    I have a situation where I have a permanent gas grill installed near a permanent underground concrete pool. At first, I was under the impression each part of the grill would need to be bonded. However, I havent been able to find anything that seems to address this in article 680. The grill is not installed yet and its possible to relocate it a little further away but I cant seem to find what that distance would be. Any ideas??
  2. #2
    Join Date
    Mar 2003
    Vermont
    Posts
    1,377
    I found this in my '17.....
    680.22B7
    (7) Low-Voltage Gas-Fired Luminaires, Decorative Fireplaces,
    Fire Pits, and Similar Equipment. Listed low-voltage gas-fi red-
    luminaires, decorative fi replaces, fi re pits, and similar equip‐
    ment using low-voltage ignitors that do not require grounding,
    and are supplied by listed transformers or power supplies that
    comply with 680.23(A)(2) with outputs that do not exceed the
    low-voltage contact limit shall be permitted to be located less
    than 1.5 m (5 ft) from the inside walls of the pool. Metallic
    equipment shall be bonded in accordance with the require‐
    ments in 680.26(B). Transformers or power supplies supplying
    this type of equipment shall be installed in accordance with the
    requirements in 680.24. Metallic gas piping shall be bonded in
    accordance with the requirements in 250.104(B) and
    680.26(B)(7).
    ~RJ~
  3. #3
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,098
    A (non attached) floating grill might be more convenient, and shouldn't need bonded to pool bonding system.
  4. #4
    Join Date
    Feb 2010
    Posts
    847
    Quote Originally Posted by romex jockey View Post
    680.22B7
    ~RJ~
    Thats perfect, thanks!
  5. #5
    Join Date
    Feb 2010
    Posts
    847
    Quote Originally Posted by kwired View Post
    Great Suggestion. Much more feasible.
  6. #6
    Join Date
    Feb 2003
    Illinois
    Posts
    23,623
    680.22B7
    ~RJ~
    I don't see how that modifies the requirement in 680.26(B)(7).
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,098
    680.22B7
    ~RJ~
    That just tells you how close it can be to the pool, if it is electrically powered. If it is non electrically powered (self powered ignitor wouldn't count) you can put it wherever you want, even in the pool. Still doesn't change bonding requirements as mentioned.
  8. #8
    Join Date
    May 2014
    AZ
    Posts
    2,324
    well, is the pool really underground? that might change things for the bbq
  9. #9
    Join Date
    Mar 2014
    Park Ridge, NJ
    Posts
    80
    From a pool design standpoint, I would never have a BBQ within 5' of a pool. There's splash out and just a plain traffic jam on the patio trying to avoid the BBQ.
    Generally permanent BBQ's are at least 10' away to allow for locating tables and chairs.
    There are definitely some backyards that are very tight and there may be no choice.
  10. #10
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,392
    Like this? I think the grill is bonded by the equipment grounding conductor routed with the supply conductors. It is safe and no further bonding is required.