    Quote Originally Posted by hbiss View Post
    Well, let's see. The interior of a raceway run outside is considered a wet location. Therefore you cannot run NM through it because NM is not listed for a wet location.

    The interior of a 3R enclosure installed outside is not considered a wet location. Breakers are not listed for wet locations.

    So here's my problem. If a raceway which is sealed up pretty damn good is considered a wet location, how is it that a 3R enclosure is considered a dry location with all it's slots and openings, none of which are even gasketed. It's like Swiss cheese in a driving rain.

    Either go to a NEMA 4 or, better yet put it inside. But the NEC, not being a design guide doesn't care if the breakers have to be replaced as long as their failure doesn't burn the house down.

    Then again what happens if corrosion prevents them from tripping?

    -Hal

    Uh..... why are you asking ME to justify what the rules are? I follow them, not make them.

    Perhaps you should ask those who MAKE the rules to explain them.

    If you have an issue with the rules, then DO SOMETHING about it.

  2. #62
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,479
    Why do you think I'm asking you to justify anything? You have nothing to do with it. I'm just stating the facts so that anybody who is interested can agree or disagree.

    The inside of the raceway rule was added because the hand wringers got all worked up about people running NM in a conduit across their front porch, it had nothing to do with the condition of the conduit in the real world.

    If there were breakers failing outdoors and houses burning we'd know about it.
    And if the Romex in conduit outside were failing and burning down houses we'd know about it too. Why are the hand wringers worried about NM in conduit and not service panels outside.

    Why not do something about it? Like AFCIs, you can offer all kinds of arguments but their mind is made up.

    -Hal
    Last edited by hbiss; 01-13-18 at 07:42 PM.

  3. #63
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,191
    Quote Originally Posted by hbiss View Post
    Why do you think I'm asking you to justify anything? You have nothing to do with it. I'm just stating the facts so that anybody who is interested can agree or disagree.

    -Hal
    Well Hal, you quoted him when expressing your opinion so that would imply you were addressing him. That is what I inferred also. Post #59.

    You may have wanted to speak to the general audience, but that is not how it totally came out.
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #64
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,479
    Ok, I see that. Didn't mean anything, I was too lazy to put it in my own words so I copy and pasted. Sorry 480.

    -Hal

  5. #65
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,060
    Quote Originally Posted by ActionDave View Post
    But if the pop cover were made of wood and covered in siding it would be perfectly acceptable, no?



    Any other purely personal ideas with overwhelming lack of evidence to support them you want to inflict on the whole country?
    Yes, it would be. What about the cover makes it 'wrong': that it's not permanently constructed (as part of the exterior wall, like you mention), that it isn't sealed well, ???

    If one used a proper weather-rated gutter under the panel, that would be fine too, yes?

    ~~~~~~

    NM coming in thru the back of the panel, while legal, is a more problematic install than it coming in thru the bottom like shown. At least with AC disconnects; every one I've seen with bad corrosion problems, the wire came in thru the back. Lack of/deteriorating caulking caused rainwater to get in and rust up everything.

    The 'pop box' shown looks like siding (or were there when the siding was installed); there is a matching piece above the panel and one covering the drop above the meter
    Electricians do it until it Hertz!

  6. #66
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,634
    I am on the Right Coast, and have never seen nor heard of the afore-mentioned pop-box. We normally use the not-legal-but-allowed-anyway PVC conduit and LB method to bring cables from the crawl space into exterior panels.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  7. #67
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    35,700
    My question is what keeps water from entering this thing in the first place?

    As a homeowner I might be more concerned where that water goes if it does enter then I am about getting a little water on the outside sheath of NM cables.

    If the thing is smaller then the panel and butted directly against panel that helps, but we get rain that travels nearly horizontal at times here.

    Any condensation that does form within panel drains to within this space also.

  8. #68
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,634
    Simple answer: never caulk the bottom edge/side of anything you attach to anything else.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  9. #69
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,191
    Quote Originally Posted by LarryFine View Post
    I am on the Right Coast, and have never seen nor heard of the afore-mentioned pop-box. We normally use the not-legal-but-allowed-anyway PVC conduit and LB method to bring cables from the crawl space into exterior panels.
    I have neither seen or heard of them till this thread. VA, NC, or MD.
    "Electricity is really just organized lightning." George Carlin


    Derek

  10. #70
    Join Date
    Jan 2009
    Location
    Port Washington, WI, USA, Earth, Etc.
    Posts
    87
    Here we call "pop" "soda", so should I ask for a soda box? Oh yeah, we have basements so we don't need them.
    You may well be the sharpest tool in the box, but in the end you are still a tool.