    Instrument connection using ICEA/NEMA Method 1

    Hi,

    For the project I am working on I need to use multi-conductor cable with a color sequence based on ICEA/NEMA Method 1 table E-2 (WITHOUT WHITE & GREEN WIRE) for control. I have to connect multiple solenoids. They have 3 connections points (2 for 120V and 1 for ground). Now my question is : What should I do with the ground connection ? If I am not mistaken, NEC code does not allow you to use another color than green but the requirements for this project are to use multi-conductors without any green wire...

    EDIT : Forgot to mention that these cables are routed in RGS conduit.

    Thanks,
    Francis

    BTW, this is my first post, I am french speaking Canadian and I have to work on multiple American projects. This forum and you guys saved my life more than often, THANK YOU !
    Last edited by GrandRoi; 01-12-18 at 07:13 PM.

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,199
    bonne journée mon ami, bienvenue!
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,973
    Francis, can the conduit and cabinets it terminates be used for the ground? If not, can you run a green conductor separate from the multi-conductor cable for the ground?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,794
    Quote Originally Posted by LarryFine View Post
    Francis, can the conduit and cabinets it terminates be used for the ground? If not,can you run a green conductor separate from the multi-conductor cable for the ground?
    I dont think the code allows a separate conductor to serve as the egc.

    I do seem to recall some dispensation on reidentification when using a m/c cable.
    Bob

  5. #5
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,794
    Quote Originally Posted by petersonra View Post
    I dont think the code allows a separate conductor to serve as the egc.

    I do seem to recall some dispensation on reidentification when using a m/c cable.
    see 200.6 (E) exception 1 for grounded conductors.

    see 250.199 (B) for ground conductors.

    These exceptions would allow you to remark a conductor in a m/c cable as white for the grounded conductor and green for the ground conductor.
    Bob