Page 2 of 2 FirstFirst 12
Results 11 to 20 of 20
Thread: 400 amp electric utility meter
  1. #11
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Quote Originally Posted by kwired View Post
    Does the meter plug in or bolt in?
    Plug in is what is called S base and is max 320 amps, bolt is K base can be 400 or 600 amps, though I have only seen about three or four of those in the wild, most POCO here are going to CT meter it if more then a 320 socket is necessary.
    K base
    Sent from my SM-G935U using Tapatalk
  2. #12
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,693
    Quote Originally Posted by codequestion View Post
    K base
    So from what I can tell you are supplying a single 400 amp service disconnecting means from this meter?
    That will mean minimum conductor size you can provide per NEC is 500 copper (provided load calculation is not over 380 amps), parallel 3/0 copper, 700 aluminum (provided load calculation is not over 375 amps), parallel 4/0 aluminum (provided load calculation is not over 360 amps).
    As I mentioned earlier if utility is installing the conductor they may go smaller yet - many here would install 350 aluminum for a 400 amp service.
  3. #13
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,194
    400A single and three phase meter base is pretty common where I have worked. In VA, POCO still provided for free. CT metering did not start till 600A.
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #14
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Utility go smaller? They dont do 500kcmil or 3/0 awg. My original question was to determine size of bonding jumpers and grounding electrode conductors. Does one look at feeder cables on the load side to service disconnect or on line side the utility feeder cables to determine grouding electrode conductor and bonding jumpers in service disconnect?
  5. #15
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,693
    GEC - look at heading in T250.66, it says "size of largest ungrounded service conductor or equivalent area for parallel conductors".
    250.102 table says same thing but is missing the word "service".
    I think if you are landing the conductor/bonding jumper in the meter you go by supply side conductor if they are different from load side conductor. If you are landing the conductor/bonding juper in the service disconnecting means - you go by the conductors that are between meter and service disconnect even if supply side of meter is different.
  6. #16
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Now going back, the utility would provide 350kcmil for 400 amp k base meter assuming it is 400 amp service? Utility would not provide 500 kcmil or 2 sets of 3/0 awg?
  7. #17
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,693
    But if you install conductors between meter an service disconnect - you inspector is going to fail if you ran 350 because you must follow NEC, even though logic tells you 350 is probably not going to overheat if it will works for them on the supply side of meter. So now you have 500 or parallel 3/0 for service entrance conductors if you are running GEC to the service disconnect.
  8. #18
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Correct. I was talking about conductors from utility transformer to utility meter. I am also calculating short circuit fault at service disconnect and was wondering typical conductor size electric utility would install for 120/208V 3 phase 400 amps base k meter. Assuming thats 400 amps service.
  9. #19
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,297
    But jumpers and grounding electrode sizes changes per nec 2014 aricle 250 based on largest unground conductor. I am after bonding jumper sizes and grounding electrode conductor based on 400 amp electric utility meter 120/208V three phase.
    see 250.66 250.102(C)(1). You are going to have to nail down the conductor size before you will know what GEC size you will need.
    Edit: sorry this was already covered. I missed the whole second page of posts.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  10. #20
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,693
    350 aluminum seems to be common, but why not ask the utility in question?
Posting Permissions
  • You may not post replies
  • You may not edit your posts