Thread: Sub-panel, MLO or Main-Breaker requirements

  1. #11
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    3,494
    Quote Originally Posted by jap View Post
    So you ordered an MDP with connector kits only but no breakers and pulled the Mains out of the subpanels to put in the MDP, then, installed lug kits back on the (4) 250 amp panels and blank covers or different dead fronts to cover the holes where the mains used to be?

    JAP>
    Exactly. And yes the AIC was adequate for them to be used at the service.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #12
    Join Date
    Jan 2007
    Posts
    3,034
    Quote Originally Posted by electrofelon View Post
    Exactly. And yes the AIC was adequate for them to be used at the service.
    What brand was the gear?

    JAP>

  3. #13
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    3,494
    Quote Originally Posted by jap View Post
    What brand was the gear?

    JAP>
    It was eaton. They were JD frame IIRC? Not too familiar with Eaton, dont usually use.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"