    Hot tub

    Hello - I am wiring a hot in Maryland and we are on the 2014 code. I would like to be able to use LFNC about 12' to the panel box and about 6' before the disconnect outside and pvc in between. From what I understand as long as I strap it accordingly I should be fine. I thought at one time I remember hearing you couldn't use more then 6' . Thanks

  2. #2
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,616
    Quote Originally Posted by John Wayne View Post
    Hello - I am wiring a hot in Maryland and we are on the 2014 code. I would like to be able to use LFNC about 12' to the panel box and about 6' before the disconnect outside and pvc in between. From what I understand as long as I strap it accordingly I should be fine. I thought at one time I remember hearing you couldn't use more then 6' . Thanks
    Wiring a "hot" what in Maryland?

    As long as the LFNC is type "B" and you secure it according to 356.30 you can do it.
    If you aim at nothing, you will hit it every time!

  3. #3
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,438
    He's wiring a hot tub. The restriction on 6' or less of LFNMC for article 680 installs went away in either 2008 or 2011 NEC.