ambient temprature correction for ac inductive reactance

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Is there a formula or table for temperature correction of ac inductive reactance?
Yes. The correction factor is 1.
The resistive portion of the complex impedance will change in the same ratio as the DC resistance, but the inductive portion can only change as a result of the mechanical expansion of the wire. I would consider that negligible.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
If the inductor is on some sort of core, then the permeability of that core will likely change with temperature, changing the inductance and the inductive reactance.

There will be no simple formula for this; you will need get data for the specific material involved.

-Jon
 

Carultch

Senior Member
Location
Massachusetts
Is there a formula or table for temperature correction of ac inductive reactance?

The NEC doesn't require you to temperature correct for resistance/reactance. The values you'll find for AC and DC resistance in Chapter 9 for your voltage drop calculations are based at 75C. And the chance that any properly sized wire will operate continuously at a hotter temperature than that, is vary rare.
 