600 amp service

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
could a 600a service be installed using a 600a disconnect with a riser with 500mcm? the service will have to be open CT metered but is it ok to be done this way?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I must be missing something !! (1)500 per phase ? What size overcurrent protection ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
(1) set of 500s per phase rated 380 amps on a 600 amp overcurrent device ? What Code section are your relying on ?
 

mannyb

Senior Member
Location
Florida
Occupation
Electrician
(1) set of 500s per phase rated 380 amps on a 600 amp overcurrent device ? What Code section are your relying on ?

LOL! I wasnt even paying attention to my own post. i was wondering what went wrong...Me!!

The service is 600a 240v single phase 3w, if i paralleled 350mcm does that sound better?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
LOL! I wasnt even paying attention to my own post. i was wondering what went wrong...Me!!

The service is 600a 240v single phase 3w, if i paralleled 350mcm does that sound better?

lot better
 