    Commercial PV conduit

    Hi,

    I'm working on a PV system that's going on a large flat roof. The city fire department said that it wants the conductors on the roof to be covered somehow so firefighters and other personnel won't trip on them. They even suggested putting the conductors under the roof (???). Would anyone be able to refer to a method or product that I could use to fulfill their request?

    Regards,
    Andy

  2. #2
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    9,434
    Quote Originally Posted by andrew.tkelly View Post
    Hi,

    I'm working on a PV system that's going on a large flat roof. The city fire department said that it wants the conductors on the roof to be covered somehow so firefighters and other personnel won't trip on them. They even suggested putting the conductors under the roof (???). Would anyone be able to refer to a method or product that I could use to fulfill their request?

    Regards,
    Andy
    That sounds capricious to me. Ask to see the regulation you would be violating.

  3. #3
    Join Date
    Mar 2015
    Location
    Berkeley, CA
    Posts
    75
    Agreed. I will ask them. Btw, I meant to say "conduit" and not "conductors".

  4. #4
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,838
    Quote Originally Posted by andrew.tkelly View Post
    . . on the roof to be covered somehow so firefighters and other personnel won't trip on them.
    What's to stop them from tripping over the covering?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  5. #5
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,315
    Quote Originally Posted by LarryFine View Post
    What's to stop them from tripping over the covering?
    ....or the gas lines on the roof, what about those?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #6
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    9,434
    Quote Originally Posted by electrofelon View Post
    ....or the gas lines on the roof, what about those?
    Or HVAC condensate lines?

  7. #7
    Join Date
    Jan 2012
    Location
    CA
    Posts
    509
    maybe little red flags, labels on conduit, upright UV resistant placards, some sort of obvious warning signs?

    Is this because you are running conduit in a setback area or where it is not allowed?

  8. #8
    Join Date
    Sep 2012
    Location
    Clinton, WA
    Posts
    74

  9. #9
    Join Date
    May 2011
    Posts
    4,194
    Quote Originally Posted by PWDickerson View Post
    One would think that putting those in setbacks or designated pathways would suffice.

    One disadvantage is that it may raise the temperature adder for the low distance to the roof, thus raising the conductor size throughout.

  10. #10
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    9,434
    Quote Originally Posted by jaggedben View Post
    One would think that putting those in setbacks or designated pathways would suffice.

    One disadvantage is that it may raise the temperature adder for the low distance to the roof, thus raising the conductor size throughout.
    I still think the OP should make the fire marshal quote the regulation he is trying to enforce. I see conduits, gas lines, condensate drip lines, etc., running all over flat rooftops all the time.