AFCI PROTECTION REQUIRED IN NURSING HOME PATIENT SLEEPING ROOMS

Status
Not open for further replies.

MasterTheNEC

CEO and President of Electrical Code Academy, Inc.
Location
McKinney, Texas
Occupation
CEO
Does NEC section 210.12 apply to sleeping rooms of a nursing home?
210.12(A) refers to Dwelling Units......a sleeping room in a nursing home would not be a dwelling unit.....Now knowing nothing about the actual "nursing home" layout and so on I will leave it at that.
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
The purveyors of exalted afci technology have already marketed a commercial afci variation.

I know this will bring much comfort to those dedicated sparks in our waning years that have all day to stare into our crotch waiting for some response.....

~RJ~
 

kwired

Electron manager
Location
NE Nebraska
210.12(A) doesn't apply unless you have a dwelling unit - typical nursing home you don't have dwelling units.

However 2014 NEC added 210.12(C) titled Dormitory Units. Read carefully and maybe even ask AHJ if they consider this to be a qualifying dormitory unit. NEC doesn't define what a dormitory unit is AFAIK.
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
Hospital Grade AFCI receptacle outlet