    i am studying for my Philadelphia masters exam and came across a question that may seem easy to many of you but it is alittle confusing to me..."which of the following may be used to insure continuity of the equipment grounding conductor in a branch circuit?" choices are a)connections to lampholders or b)terminals of receptacles. I would say you can use both assuming that the receptacle and lampholder have an equipment grounding conductor terminal. am I correct in my assumption?
  2. #2
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,969
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    A receptacle has only one terminal listed for only one conductor so it cannot be used for continuity of the EGC.
    Rob
  3. #3
    Join Date
    Mar 2016
    philadelphia,pa
    Posts
    109
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I don't quite understand? if you put your test leads on the neutral terminal and the grounding terminal wouldn't you be able to read continuity back at the panel?
  4. #4
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by journeyman0217 View Post
    Yes, neutral and ground at a receptacle will show continuity when you put meter leads on them. That said, you cannot use the ground (green) screw terminal of a receptacle to maintain continuity for the grounding pathway. If you have 2 or more cables or ground wires entering a jbox, the grounds must be tied together and a pigtail run the the receptacle. Removing the receptacle cannot break the grounding pathway. If it's pigtailed to, removing that pigtail still keeps the circuit's ground path intact. Code section 250.148:
    https://www.jadelearning.com/jadecc/...p?imDif=3073.0
  5. #5
    Join Date
    Mar 2016
    philadelphia,pa
    Posts
    109
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    so as far as the receptacle terminal goes the answer would be no...would that apply to the lampholder as well? the question to me is vague....
  6. #6
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,349
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I think the question stinks. I would say both since removing either does not change the continuity of the equipment grounding conductor. Not sure if that is what they are after or not
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  7. #7
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Correct. The answer is no. You cannot use the receptacle terminal to insure continuity of the EGC per 250.148. If there are just the two choices, then by default A is the only answer since we eliminated B.
    Which of the following may be used to insure continuity of the equipment grounding conductor in a branch circuit?:
    A) Connections of lampholders
    B) Terminals of receptacles
    Lampholders do not typically have a place to land the grounds, if anything they have a wago installed to a small braided wire to the light. I dont believe there is a NEC code that prohibits using a lampholder for EGC continuity like there is for receptacles.
  8. #8
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,687
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    To me, the correct answer is neither.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  9. #9
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,969
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    I agree, there is nothing wrong with the question except that the correct answer is not on the list.
    250.148(B) Grounding Continuity. The arrangement of groundingconnections shall be such that the disconnection or theremoval of a receptacle, luminaire, or other device fed fromthe box does not interfere with or interrupt the groundingcontinuity.
    Rob
  10. #10
    Join Date
    Jan 2012
    Suburbs of Chicago
    Posts
    170
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A & b are the only choices available? Is a lamp holder considered a luminaire, and thereby also prohibited?