Page 4 of 4 FirstFirst ... 234
Results 31 to 37 of 37

Thread: Insulation piercing connector guidance needed

  1. #31
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,315
    That creep has a wife?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #32
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    9,434
    Quote Originally Posted by electrofelon View Post
    That creep has a wife?
    Not any more; the school bus going over the cliff killed her. Didn't you read the thread?

  3. #33
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    1,486
    Quote Originally Posted by electrofelon View Post
    That creep has a wife?
    yes, but I've always suspected it was not of her own free will.

  4. #34
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,315
    Quote Originally Posted by Coppersmith View Post
    They charge you a fee? I have three POCOs in my service area none of which charge a fee. Is this common?

    ETA: If they are charging a fee on the HO bill, I have never heard about it (or been yelled at about it).
    I don't really know. I rarely get a D/R. I had to get one for PSE out here near Seattle. I could have sworn it was $100 or so.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  5. #35
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,838
    Quote Originally Posted by ggunn View Post
    Who just happened to be the wife of Kim Jong-un, killing her and the heir to the North Korean dictatorship and thereby triggering a global thermonuclear war.
    And the green grass grew all around, all around, and the green grass grew all around.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  6. #36
    Join Date
    Sep 2012
    Location
    Clinton, WA
    Posts
    74
    The spec sheet for the Ilsco product in questions states the following:
    [COLOR=rgb(13.700000%, 12.200000%, 12.500000%)]
    Contains no external energized parts. Can be installed “hot” on energized
    [/COLOR]


    [COLOR=rgb(13.700000%, 12.200000%, 12.500000%)]conductors providing tap conductor is not under load.
    [/COLOR]





    We prefer to use the Burndy BIBD-350-2 insulated taps. It is big enough to slide over the insulation of a 4/0 wire, so you don't have to cut the line conductor. We always call for a disconnect/reconnect when we do a line-side tap. PSE only charges $37 for a meter pull, and they are always out the same day to re-connect. No reason to do anything else.

  7. #37
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    543
    Quote Originally Posted by Coppersmith View Post
    I've been asked to do a job installing a supply side tap for a PV system. The spec calls for using the product below or similar:

    https://commerce.ilsco.com/e2wShoppi...ink=2100001183

    I've never installed one of these. Can it be installed hot? Is it safe to do so? Is the bolt insulated from the wire?

    Keep in mind that OSHA takes a dim view of working hot if it's not justified. Check OSHA 1910.333(a)(1) for what is considered a justification and notice that cost savings, time savings, or "the other guy does it" are not listed as justifications to work hot. If an accident happens to an employee you will be swinging in the wind.