    Motor Current

    What's the formula to determine motor current when horsepower and voltage are known? I'm trying to solve a problem where the answer uses I = 600*HP/V, but I can't for the life of me find this equation anywhere else. Any ideas?

    Thanks

  2. #2
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,573
    180206-2407 EST

    pcboiler:

    Quite often a fully loaded motor might have a rough estimate of of 1000 VA input for 1 HP of mechanical output. This covers power factor and motor efficiency. At 100% efficiency 1 HP = 746 W.

    Your equation is more like 600 VA = 1 HP. This is not possible as a motor On the other hand if you supplied 1 HP to a generator and it could produce 600 VA output, then that is possible. That would be 80% efficiency.

    .

  3. #3
    Join Date
    Dec 2008
    Posts
    482
    In my opinion, V it is line-to-neutral in a three phase system then from HP to W the factor is
    1/.746*1000/3 and the product between power factor and efficiency [average]=0.745:
    I=HP/.746*1000/3/.745/V=599.8*HP/V

  4. #4
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    7,320
    My guess is that this formula was for guesstimating starting current on a motor; 600% is a usual value to use for that. But simply dividing HP by voltage doesn’t get you to FLA, and the percent sign may have been lost in the fog of time. So it might have originally been 600% of kVA/V, or even 600% of kW/V, which would be an over-estimated way to be sure you were covered, because by leaving out power factor, you are going to end up with a higher value and if using this to quickly estimate the size of a service or generator, it’s a safer bet. It’s nothing that is officially sanctioned anywhere though, it sounds more like a “rule of thumb” issue no matter what.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  5. #5
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    7,320
    Quote Originally Posted by Julius Right View Post
    In my opinion, V it is line-to-neutral in a three phase system then from HP to W the factor is
    1/.746*1000/3 and the product between power factor and efficiency [average]=0.745:
    I=HP/.746*1000/3/.745/V=599.8*HP/V
    Oh that’s clever. But it would only apply to single phase motors connected L-N in a 3 phase Y system. Given that’s the way most of the rest of the world is configured; 400Y230V (nominal), that would make sense.

    But it doesn’t work here in North America unless it’s a 208Y120 service and a 120V motor. (Technically it could apply to a 480Y277 service, but 277V motors are rarely used).
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  6. #6
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,755
    I use

    i = (HP X 746)/(sqrt3 x 0.95 x 0.8 x V)
    i = 565 x HP/V
    0.95 for line V vs motor V ie 480 vs 460
    0.8 ~ pf x eff

    the likely used a smaller number for pf x eff



  7. #7
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,327
    Quote Originally Posted by Ingenieur View Post
    I use

    i = (HP X 746)/(sqrt3 x 0.95 x 0.8 x V)
    i = 565 x HP/V
    0.95 for line V vs motor V ie 480 vs 460
    0.8 ~ pf x eff

    the likely used a smaller number for pf x eff
    Yes, that is the way. JuliusRight divided HP by 746 instead of multiplying it to find watts.
    And still more hilarious jraef objection to it.
    Last edited by Sahib; 02-07-18 at 12:32 PM.

  8. #8
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,755
    Quote Originally Posted by Sahib View Post
    Yes, that is the way. JuliusRight divided HP by 746 instead of multiplying it to find watts.
    And still more hilarious jraef objection to it.
    100 hp motor 480/3
    my way 118
    NEC 124

    pretty close



  9. #9
    Join Date
    Dec 2008
    Posts
    482
    [QUOTE=Sahib;1893596]Yes, that is the way. JuliusRight divided HP by 746 instead of multiplying it to find watts.
    Thanks.I was Julius.. Wrong!

  10. #10
    Join Date
    Feb 2018
    Location
    Chicago
    Posts
    2
    Quote Originally Posted by Ingenieur View Post

    i = (HP X 746)/(sqrt3 x 0.95 x 0.8 x V)
    i = 565 x HP/V
    0.95 for line V vs motor V ie 480 vs 460
    0.8 ~ pf x eff

    the likely used a smaller number for pf x eff
    Nice! That must be it.

    Thanks
    Last edited by pcboiler; 02-09-18 at 10:41 PM.