    Generator breaker sizing

    I have emergency generator 200kva, 480V, 3 phase. What would be appropriate overcurrent size for the emergency generator per Nec 2014?

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    384
    I have emergency generator 200kva, 480V, 3 phase. What would be appropriate overcurrent breaker size (OCPD) for the emergency generator per Nec 2014?



    Sent from my SM-G935U using Tapatalk

  3. #3
    Join Date
    Sep 2004
    Location
    Vancouver, WA
    Posts
    675

    Manufacturer

    The generator manufacturer will have a standard OCPD for the generator.
    e^(i pi) = -1

  4. #4
    Join Date
    May 2007
    Location
    Westminster, MD
    Posts
    599
    276 amps, so a 300-amp breaker with 300-amp cable.

  5. #5
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    384
    Quote Originally Posted by beanland View Post
    The generator manufacturer will have a standard OCPD for the generator.
    Yea but in my case I have to update the emergency generator load and so I was wondering what the new circuit breaker size be. I have 225 amps ATS downstream.

    Sent from my SM-G935U using Tapatalk

  6. #6
    Join Date
    May 2007
    Location
    Westminster, MD
    Posts
    599
    Quote Originally Posted by codequestion View Post
    Yea but in my case I have to update the emergency generator load and so I was wondering what the new circuit breaker size be. I have 225 amps ATS downstream.

    Sent from my SM-G935U using Tapatalk
    Then there's your answer, 225 amps. Just make sure there's less than 225 amps of load at any given time.

  7. #7
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    384
    Quote Originally Posted by mayanees View Post
    Then there's your answer, 225 amps. Just make sure there's less than 225 amps of load at any given time.
    Their was change order. Ats is now 250 amps. So FLA is less than 250 amps. How does this work in terms of sizing breaker?

    Sent from my SM-G935U using Tapatalk

  8. #8
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,873
    Quote Originally Posted by codequestion View Post
    Their was change order. Ats is now 250 amps. So FLA is less than 250 amps. How does this work in terms of sizing breaker?

    Sent from my SM-G935U using Tapatalk
    When you get all the changes in order come back and start a new thread with all the correct information.

    Roger