    I agree that the storage space is not the entire closet. The Halo RL56 series specifically state they comply with 410.16(C)(5) which allows fixtures identified for use in the storage space.

    410.16(C)(5)
    Surface-mounted fluorescent or LED luminaires shall be
    permitted to be installed within the closet storage space
    where identified for this use.
    Curt Swartz
    Electrical Contractor

  2. #12
    Join Date
    Jul 2013
    Location
    Boston, Massachusetts, USA
    Posts
    81
    Quote Originally Posted by curt swartz View Post
    The Halo RL56 series specifically state they comply with 410.16(C)(5) which allows fixtures identified for use in the storage space.
    Indeed! The webpage makes that claim, while the spec sheet speaks instead of 410.16(C)(3).

    I asked Copper for clarification, and will report back, if I get a reply.