    240.5(B)(2), (1),(2)

    Article 240.5(B)(2), (1),(2) I find this confusing. This part of the article deals with overcurrent protection for fixture wire and states "Fixture wire shall be permitted to be tapped to the branch-circuit in accordance with the following:
    (1) 20-ampere circuits - 18 AWG, up to 15m (50 ft) of run length.
    (2) 20 ampere circuits - 16 AWG, up to 30m (100 ft) of run length.

    Does this mean that the total amount of #18 AWG you could use is 50 ft? Or does it mean that any run cannot exceed 50 ft? Could you feed as many lights as you wanted with #18 AWG fixture whips as long as they are under 50ft?

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,173
    Up to 50' means no more than 50'. This allows you to run fixture wires through a long row of end to end fixtures and not have to carry the full size branch circuit conductors all the way through. Your connected load just cannot exceed the conductor ampacity in Table 402.5.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,195
    This older thread seems to follow what Infinity just posted.

    http://forums.mikeholt.com/showthread.php?t=179488
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,580
    Quote Originally Posted by infinity View Post
    Up to 50' means no more than 50'. This allows you to run fixture wires through a long row of end to end fixtures and not have to carry the full size branch circuit conductors all the way through. Your connected load just cannot exceed the conductor ampacity in Table 402.5.
    So you are saying that there is only one outlet in that example and the conductors run inside the fixture are not branch circuit conductors? It is my opinion that where the conductors serve more than one fixture, they are branch circuit conductors and you cannot use the fixture wire provisions.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,173
    Quote Originally Posted by PeterjOBrien View Post
    (1) 20-ampere circuits - 18 AWG, up to 15m (50 ft) of run length.
    (2) 20 ampere circuits - 16 AWG, up to 30m (100 ft) of run length.
    Quote Originally Posted by don_resqcapt19 View Post
    So you are saying that there is only one outlet in that example and the conductors run inside the fixture are not branch circuit conductors? It is my opinion that where the conductors serve more than one fixture, they are branch circuit conductors and you cannot use the fixture wire provisions.
    If that were the case how would you ever use 50' or 100' of conductor as mentioned in the OP?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,580
    Quote Originally Posted by infinity View Post
    If that were the case how would you ever use 50' or 100' of conductor as mentioned in the OP?
    One long fixture whip. I see anything that feeds more than one fixture as being part of the branch circuit.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)