    Quote Originally Posted by jumper View Post
    No, it would make no sense.
    Main breaker in panel not even required. You have a main service OCPD in the fused disco. It is protecting the panel already.
    Think about it.
    Well main in breaker in panel is to protect the panel.
    Sent from my SM-G935U using Tapatalk
  2. #32
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,319
    Quote Originally Posted by codequestion View Post
    if you have a fused disco, you don't need a MB panel, just main lug.
    edit: unless you needed to protect the panel per 408.36, but you should coordinate the panel rating with the fuses in the disco.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #33
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,196
    Panel is double protected. Fuses and breaker-twice. Overkill, not a problem, but waste of money.
    Fuses protect feeder (from disco) and panel. A MLO panel would work. Think about it.....
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #34
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,612
    Many times I can buy a main breaker panel with breakers (contractor pack) cheaper than a MLO panel. That's counting having to buy breakers separate for the MLO.
    If you aim at nothing, you will hit it every time!
  5. #35
    Join Date
    Jun 2004
    Posts
    4,319
    Quote Originally Posted by Little Bill View Post
    Single phase, for sure. Three phase, def not. Don't remember if OP said what this is.
  6. #36
    Join Date
    Jan 2009
    Posts
    14,196
    My point was double protection not needed. Breaker is superfluous.
    How about waste of resources?
    Derek
  7. #37
    Join Date
    Jan 2009
    Posts
    14,196
    Quote Originally Posted by electrofelon View Post
    400A 208Y/120V 3 phase.
    Derek
  8. #38
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,443
    If you have a fused disco it's already protected.
  9. #39
    Join Date
    Jan 2009
    Posts
    14,196
    Am I the only one who gets a little disoriented every time I glance at Rob’s picture?
    The black stripes seem to twist. Kinda cool really.
    Derek
  10. #40
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,848
    Which picture is that?