Thread: Disconnecting means

  1. #41
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,820
    Quote Originally Posted by LarryFine View Post
    Which picture is that?
    Service conductors encased in concrete post #21.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #42
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,218
    Quote Originally Posted by LarryFine View Post
    Which picture is that?
    Big yellow duct work, black stripes.

    Edit: “Which” not “what.” Doh!
    Last edited by jumper; 02-11-18 at 07:12 PM.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #43
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,781
    Quote Originally Posted by jumper View Post
    Am I the only one who gets a little disoriented every time I glance at Rob’s picture?

    The black stripes seem to twist. Kinda cool really.
    Focus Grasshopper!
    If you aim at nothing, you will hit it every time!

  4. #44
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,218
    Quote Originally Posted by Little Bill View Post
    Focus Grasshopper!
    I’m completely focused darn it!

    Red Green was a great show IMO!!!
    "Electricity is really just organized lightning." George Carlin


    Derek

  5. #45
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,630
    Quote Originally Posted by jumper View Post
    Panel is double protected. Fuses and breaker-twice. Overkill, not a problem, but waste of money.

    Fuses protect feeder (from disco) and panel. A MLO panel would work. Think about it.....
    Last week I needed to replace a 200 amp three phase loadcenter type panelboard. The existing one was MB but there was also a service disconnect breaker outside. I knew the breaker was out there, but I completely spaced when it came time to order one and I ordered a MB instead of MLO panel to replace it I blame the originally installer who for some reason un-necessarily installed a MB panel which put MB in the front of my mental rolodex.

    Edit to add: The outside MB was bad, it wouldn't shut off. It would have been $700-$800 to replace. I found a new surplus one on ebay, saved the client $350, so I guess all in all we are about even
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #46
    Join Date
    Jan 2007
    Posts
    3,660
    Quote Originally Posted by jumper View Post
    No, it would make no sense.

    Main breaker in panel not even required. You have a main service OCPD in the fused disco. It is protecting the panel already.

    Think about it.
    Where's the rule that states if the service disconnect is not attached to the structure you have to have a disconnect at the building also?

    I cant find it.


    JAP>

  7. #47
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,566
    Quote Originally Posted by jap View Post
    Where's the rule that states if the service disconnect is not attached to the structure you have to have a disconnect at the building also?

    I cant find it.


    JAP>

    I think this is what you are looking for. The problem here is that outside the building is ambiguous.

    230.70(A) Location. The service disconnecting means shall be installed
    in accordance with 230.70(A)(1), (A)(2), and (A)(3).
    (1) Readily Accessible Location. The service disconnecting
    means shall be installed at a readily accessible location either
    outside of a building or structure or inside nearest the point of
    entrance of the service conductors.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  8. #48
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    443
    Quote Originally Posted by jap View Post
    Where's the rule that states if the service disconnect is not attached to the structure you have to have a disconnect at the building also?

    I cant find it.


    JAP>
    There is no rule that requires the service disconnect to be attached to the structure.

  9. #49
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,566
    Quote Originally Posted by jap View Post
    Where's the rule that states if the service disconnect is not attached to the structure you have to have a disconnect at the building also?

    I cant find it.


    JAP>
    Sorry I think this is more accurate

    225.32 Location. The disconnecting means shall be installed
    either inside or outside of the building or structure served or
    where the conductors pass through the building or structure.
    The disconnecting means shall be at a readily accessible location
    nearest the point of entrance of the conductors. For the
    purposes of this section, the requirements in 230.6 shall be
    utilized.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  10. #50
    Join Date
    Jan 2007
    Posts
    3,660
    Quote Originally Posted by Dennis Alwon View Post
    Sorry I think this is more accurate
    So if the meter and fused disconnect were on a rack out in the lot nowhere near the structure another disconnect would not be required at the structure itself?



    JAP>