    Quote Originally Posted by jap View Post
    So if the meter and fused disconnect were on a rack out in the lot nowhere near the structure another disconnect would not be required at the structure itself?
    JAP>
    Short answer "yes".
    In "real life" Ive the the answer vary by AHJ and by distance how close the two are.
    "Nowhere near" will likely mean disconnect at both
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  2. #52
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,933
    For services over 300 V PH-PH our POCO requires a disconnect ahead of the meter, I typically use a non fused disconnect if the short circuit current is <10,000 Amps.
    Then on the load side we install a fused disconnect, this is service disconnect.
    Moderator-Washington State
    Ancora Imparo
  3. #53
    Join Date
    Jan 2007
    Posts
    3,660
    Quote Originally Posted by augie47 View Post
    Short answer "yes".
    What is the rule that would require a disconnect at both locations?
    JAP>
  4. #54
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,629
    JAP>
    225.33
    Edit: actually 230 would apply to one, 225 for the second.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  5. #55
    Join Date
    Jan 2007
    Posts
    3,660
    Quote Originally Posted by electrofelon View Post
    225.33
    Lot of variables.
    JAP>
  6. #56
    Join Date
    Jan 2007
    Posts
    3,660
    As to whether his panel needs a main in it or not at the building that is.