    Disconnecting means
    Does a non fused disconnect switch loacted first device on load end of utility meter qualify as service disconnecting means?
    Sent from my SM-G935U using Tapatalk
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,629
    Quote Originally Posted by codequestion View Post
    Yes. In fact it has to be. There is no other option. But you will need overcurrent protection right next to it. Make sure you have 10K fault current or less.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #3
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Quote Originally Posted by electrofelon View Post
    I have first device on load end of utility meter is non fused disconnect. Downstream load end of the non fused disconnect first device is panelboard with main breaker. Would that be overcurrent protection right next to non fused disconnect or you are talking about something else?
  4. #4
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,218
    Is the disconnect rated as Suitable for Use as Service Equipment (SUSE)? Has to be marked as such.
    "Electricity is really just organized lightning." George Carlin
    Derek
  5. #5
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Quote Originally Posted by jumper View Post
    Where would I find non fused disconnect rated for use as service equipment?
  6. #6
    Join Date
    Jun 2004
    Posts
    4,629
    Don't have my code book in front of me but IIRC the wording is the OCPD must be "integral or immediately adjacent to" the service disconnect. What is the purpose of the disco?
  7. #7
    Join Date
    Jan 2009
    Posts
    15,218
    230.91
    230.91 Location. The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto.
    Derek
  8. #8
    Join Date
    Jun 2004
    Posts
    4,629
    A supply house.
  9. #9
    Join Date
    Jan 2009
    Posts
    15,218
    Derek
  10. #10
    Join Date
    Jun 2004
    Posts
    4,629
    230.91
    "thereto"...dammit, always get that wrong
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts