  1. #1

    PIGTAILS AT RECEPTACLES

    Is a smaller gauge wire allowed for a pigtail. ex: on a 20 recpt can 14 awg be used as a pigtail? My reading of 210.19(A)(4) would say No.

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,838
    I would agree with your reading.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,188
    The pigtails need to match the size of the OCPD or be larger. You could have a #8 pigtail on a 40 amp circuit with a single 50 amp receptacle.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4

    RECEPTACLES PIGTAILS PART 2

    Quote Originally Posted by Joseph Alexander View Post
    Is a smaller gauge wire allowed for a pigtail. ex: on a 20 recpt can 14 awg be used as a pigtail? My reading of 210.19(A)(4) would say No.
    Ive had the argument that this is a tap (NOT!) but I was wondering about, since the pigtail is typically THHN 14 it is rated by 310.15 as 20-25 amps, would this allow the 14 awg pigtail on a 20 amp circuit?

  5. #5
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,195
    Quote Originally Posted by Joseph Alexander View Post
    Ive had the argument that this is a tap (NOT!) but I was wondering about, since the pigtail is typically THHN 14 it is rated by 310.15 as 20-25 amps, would this allow the 14 awg pigtail on a 20 amp circuit?
    No, small breaker rules, 240.4(D)
    "Electricity is really just organized lightning." George Carlin


    Derek

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,188
    Quote Originally Posted by Joseph Alexander View Post
    Ive had the argument that this is a tap (NOT!) but I was wondering about, since the pigtail is typically THHN 14 it is rated by 310.15 as 20-25 amps, would this allow the 14 awg pigtail on a 20 amp circuit?
    The ampacity of a #14 pigtail is 15 amps so you cannot exceed a 15 amp OCPD. Jumper gave you the code reference.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,758
    If this were HID luminaires it is possible to do what OP mentioned. See 410.62(C)(2). could have a 50 amp circuit with lesser rated receptacles tapped to that circuit for the luminaires. Tap conductor and receptacle in such application only needs to be 125% or luminaire rated current.

    Most other applications not allowed though.