Thread: Generator Remote Stop Location

  1. #11
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    1,215
    Quote Originally Posted by kwired View Post
    Valve in fuel line count as a EPO?
    No. Prime mover shutdown must kill the mover electrically.

    Like shutting the key off in your car, it stops running and won't start.

  2. #12
    Join Date
    Mar 2014
    Location
    South Florida
    Posts
    215
    is the generator is its own building or room? put yourself in a fire fighters shoes. Where will they likely approach from? put it there.

    another option is to talk to the local fire marshal about it, after doing your research.

  3. #13
    Join Date
    Feb 2017
    Location
    Nashville
    Posts
    14
    Quote Originally Posted by texie View Post
    This is an area that it will depend on your NEC version. There are some new requirements for 2017. See 445.18.
    Can you quote the important parts of this section? I just looked at 2014 and that's what's applicable for this project. However I'm very curious what 2017 says. Thanks!

  4. #14
    Join Date
    May 2007
    Location
    Westminster, MD
    Posts
    614
    Quote Originally Posted by mh06670 View Post
    Can you quote the important parts of this section? I just looked at 2014 and that's what's applicable for this project. However I'm very curious what 2017 says. Thanks!
    445.18 Disconnecting Means and Shutdown of Prime Mover.
    (A) Disconnecting Means. Generators other than cord-and-plug-connected portable shall have one or more disconnecting means. Each disconnecting means shall simultaneously open all associated ungrounded conductors. Each disconnecting means shall be lockable in the open position in accordance with 110.25.
    (B) Shutdown of Prime Mover. Generators shall have provisions to shut down the prime mover. The means of shutdown shall comply with all of the following:
    (1) Be equipped with provisions to disable all prime mover start control circuits to render the prime mover incapable of starting
    (2) Initiate a shutdown mechanism that requires a mechanical reset

    The provisions to shut down the prime mover shall be permitted to satisfy the requirements of 445.18(A) where it is capable of being locked in the open position in accordance with 110.25.

    Generators with greater than 15 kW rating shall be provided with an additional requirement to shut down the prime mover. This additional shutdown means shall be located outside the equipment room or generator enclosure and shall also meet the requirements of 445.18(B)(1) and (B)(2).

  5. #15
    Join Date
    Feb 2017
    Location
    Nashville
    Posts
    14
    Quote Originally Posted by mayanees View Post
    445.18 Disconnecting Means and Shutdown of Prime Mover.
    (A) Disconnecting Means. Generators other than cord-and-plug-connected portable shall have one or more disconnecting means. Each disconnecting means shall simultaneously open all associated ungrounded conductors. Each disconnecting means shall be lockable in the open position in accordance with 110.25.
    (B) Shutdown of Prime Mover. Generators shall have provisions to shut down the prime mover. The means of shutdown shall comply with all of the following:
    (1) Be equipped with provisions to disable all prime mover start control circuits to render the prime mover incapable of starting
    (2) Initiate a shutdown mechanism that requires a mechanical reset

    The provisions to shut down the prime mover shall be permitted to satisfy the requirements of 445.18(A) where it is capable of being locked in the open position in accordance with 110.25.

    Generators with greater than 15 kW rating shall be provided with an additional requirement to shut down the prime mover. This additional shutdown means shall be located outside the equipment room or generator enclosure and shall also meet the requirements of 445.18(B)(1) and (B)(2).
    Thanks!


    Sent from my iPhone using Tapatalk

  6. #16
    Join Date
    May 2018
    Location
    Mass
    Posts
    1
    445.18 requires prime mover shutdown device located outside generator room for indoor installations or outside of the enclosure for exterior installations. Best bet would be to ask your inspector what he considers an “enclosure “ but generally speaking weatherproof cabinet or enclosure.