    SHORE POWER AND RESI LOAD CALC

    Hello all and thanks for lookin at my post!

    I am doing a residential load calc.

    They have 2 shore power connections rated at 30A / 240V. (They do have 2 boats with unknown loads.)

    I am inclined to use both at full value in my calc.

    This pushes the calc way up over 200.

    Am I making a mistake?

    Thanks!

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,195
    Look at 555.12.

    The article does not say resi, but in the 2017 it has been changed and does.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Apr 2011
    Location
    Pinellas Park, Florida
    Posts
    106
    Quote Originally Posted by jumper View Post
    Look at 555.12.

    The article does not say resi, but in the 2017 it has been changed and does.
    THANKS!

    Looks like 2 receps with one each in 2 slips would be 100% per the change you stated in 2017. (2011 and 2014 NEC marina and boatyards to include residential. We are still on 2011 here)

    Someone just got a service upgrade!
    Last edited by florida-sparkey; 02-12-18 at 02:05 PM.

  4. #4
    Join Date
    Apr 2011
    Location
    Pinellas Park, Florida
    Posts
    106
    Quote Originally Posted by jumper View Post
    Look at 555.12.

    The article does not say resi, but in the 2017 it has been changed and does.
    BTW - That is an important change because 2014 SCOPE states it is not for use with single family dwellings.