    Unit heaters

    Can 2 3kw 1ph 208v heaters be installed on 1 circuit? I remember seeing something about 30a max breaker in 424 of NEC.

  2. #2
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by toomunsch View Post
    Can 2 3kw 1ph 208v heaters be installed on 1 circuit? I remember seeing something about 30a max breaker in 424 of NEC.
    No because each heater draws 14.4A, and 28.8A is too much as a continuous load on a 30A breaker. Heating loads are considered continuous so you are limited to 24A (80%) on a 30A breaker. You'll need 2 20A circuits.
    Electricians do it until it Hertz!

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,167
    Are the units listed at 3kw for 208v or at 240V. This would make a difference
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,758
    Quote Originally Posted by toomunsch View Post
    Can 2 3kw 1ph 208v heaters be installed on 1 circuit? I remember seeing something about 30a max breaker in 424 of NEC.
    Correct on the 30 amp - see 424.3. Circuits supplying multiple units are limited to 30 amps, though if it is an infrared heater in other then dwelling, it can be on 50 amp circuit.

  5. #5
    Join Date
    Mar 2007
    Posts
    16
    I don't have the guts yet but I think they are just resistive heaters. Thx for the input

  6. #6
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by Dennis Alwon View Post
    Are the units listed at 3kw for 208v or at 240V. This would make a difference
    You're correct. If they are 3kw @ 240V, they will draw 10.8A ea on 208V, tho the output will be reduced to ~2.3kW. Both could be on one 30A circuit.
    Electricians do it until it Hertz!