    Quote Originally Posted by DBoone View Post
    I will be going back tomorrow to meet with my floor guy. I will check the receptacle. Any good way to trace down the other end of the cable besides opening up kitchen counter boxes, undo the connections and check continuity with my meter?
    Sure. De-energize the circuit and push a fish-tape in the conduit and listen for the end to hit the inside of a box nearby, maybe with the help of a second person.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  2. #12
    Join Date
    Feb 2018
    Location
    iowa, usa
    Posts
    61
    Quote Originally Posted by DBoone View Post
    I will be going back tomorrow to meet with my floor guy. I will check the receptacle. Any good way to trace down the other end of the cable besides opening up kitchen counter boxes, undo the connections and check continuity with my meter?
    Here is a cheap Klein Digital circuit breaker finder that sells for $41.37.
    It should also indicate the hot contact of receptacles upstream of the island receptacle the transmitter is plugged into. I do know the several hundred dollar circuit/breaker finders do. Touch the receiver against the hot (smaller slot) of the face of the receptacle.

    https://www.homedepot.com/p/Klein-To...T300/202330830

    https://data.kleintools.com/sites/al...structions.pdf

  3. #13
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,246
    Won't a breaker finder indicate at every receptacle on the circuit?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  4. #14
    Join Date
    Feb 2018
    Location
    iowa, usa
    Posts
    61
    Quote Originally Posted by LarryFine View Post
    Won't a breaker finder indicate at every receptacle on the circuit?
    Yes, up stream. In a kitchen how many outlets can there be on the circuit?

  5. #15
    Join Date
    Feb 2018
    Location
    iowa, usa
    Posts
    61
    Quote Originally Posted by LarryFine View Post
    Sure. De-energize the circuit and push a fish-tape in the conduit and listen for the end to hit the inside of a box nearby, maybe with the help of a second person.
    Caution: What if the de-energized circuit is part of a multi-wire branch circuit? The box the fish tape is pushed into could have the hot from the other circuit of the multi-wire branch circuit made up on an outlet.

  6. #16
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    22,246
    Quote Originally Posted by Jamesco View Post
    Caution: What if the de-energized circuit is part of a multi-wire branch circuit? The box the fish tape is pushed into could have the hot from the other circuit of the multi-wire branch circuit made up on an outlet.
    So, de-energize them all, if not on a 2-pole breaker.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  7. #17
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,748
    Quote Originally Posted by LarryFine View Post
    So, de-energize them all, if not on a 2-pole breaker.

    It is possible, though not likely, for there to be two independent circuits in a box even if neither of them is an MWBC.

  8. #18
    Join Date
    Feb 2013
    Location
    Mississippi
    Posts
    300
    Thanks everyone for the advice and suggestions. I will keep you updated.