    #3 for 100 amp service in commercial building

    Can #3 cu be used for 100 amp service in a commercial building?

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    14,196
    Quote Originally Posted by hardworker View Post
    Can #3 cu be used for 100 amp service in a commercial building?
    In general, yes. Why do you think it may not?

    Any details we should know for a more complete answer?
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,197
    Under normal conditions #3 THHN is a 100 amp conductor in T310.15(B)(16).
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,786
    Unless ampacity adjustments are necessary#3 is a 100 amp conductor @ 75C.