receptacle type for christmas lighting on top of municipal poles.

Status
Not open for further replies.

rh4245

Member
Location
Nescopeck PA
I believe the NEC has an exception of the use of GFCI receptacles and the grounding requirement for receptacles located out of reach of the public and fed via overhead conductors. Any comments or help is appreciated.
 

rh4245

Member
Location
Nescopeck PA
The argument I am getting is that the NEC is not requiring GFCI protected receptacles outside of commercial buildings and the poles, although not part of the building, are outside the commercial building.
 

growler

Senior Member
Location
Atlanta,GA
The argument I am getting is that the NEC is not requiring GFCI protected receptacles outside of commercial buildings and the poles, although not part of the building, are outside the commercial building.


What code cycle are you on? There was a time when GFCI protection wasn't needed for commericial receptacles but it was not a good idea.
 