    Approved wiring for under-cabinet lights

    I believe this has been discussed here in the forum in the past but I couldn't find an answer in the archives. An EC friend of mine asked me what type of "in wall" wiring is approved for LED under-cabinet strip lights. He said he ran two # 14 NMC whips into the basement for switching and the LED driver would be located there. The wiring to the LED strip lights will be 12 volts. Is there a structured cable that is now approved for "in wall" use for this application ?

    Thanks.

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,660
    The wire I use is rated Class 2 and 3 but I believe it needs to be class 2. Technically, nm cable is non compliant which seems odd to me
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,493
    Thanks Dennis. Do you have a manufacturer or part # ?

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,660
    I don't think so but let me see if I can find it
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #5
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,493
    Thanks. Pleasse don't go nuts.

  6. #6
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,660
    Honeywell Genesis Cable 52525506

    Here is the Honeywell Cable # 800-222-0060

    I have both the 12/2 and 14/2. In most cases the 14/2 should be fine
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  7. #7
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,493
    Thank you.

  8. #8
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    24,378
    Quote Originally Posted by Dennis Alwon View Post
    Technically, nm cable is non compliant which seems odd to me
    Why is that?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  9. #9
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,660
    Quote Originally Posted by infinity View Post
    Why is that?
    Because if you are using a class 2 trany then , my understanding you must use class 2 wiring. If you use chapter 3 wiring methods then you must install it in a chapter 3 approved means.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    34,756
    Quote Originally Posted by Dennis Alwon View Post
    Because if you are using a class 2 trany then , my understanding you must use class 2 wiring. If you use chapter 3 wiring methods then you must install it in a chapter 3 approved means.
    411.6(D) (2014 NEC)

    (D) Insulated Conductors.
    Exposed insulated secondary circuit conductors shall be of the type, and installed as, described in (1), (2), or (3):


    (1) Class 2 cable supplied by a Class 2 power source and installed in accordance with Parts I and III of Article 725.


    (2) Conductors, cord, or cable of the listed system and installed not less than 2.1 m (7 ft) above the finished floor unless the system is specifically listed for a lower installation height.


    (3) Wiring methods described in Chapter 3
    NM cable falls under (3).