    More than one wire under a screw terminal

    Name:  20180213_131113.jpg
Views: 1313
Size:  139.0 KB

    Type MC-HL cable has 3 ground wires. Do you think this is a code violation? Or is it ok to twist together and land.
    If the women dont find you handsom, at least they will fine you handy

  2. #2
    Join Date
    Jan 2007
    Posts
    3,660
    I'd start all over.

    JAP>

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,927
    Not familiar with the cable in question, but something tells me the three together must be used as one EGC - so that sort of makes it one conductor? Kind of like the concentric bare conductor in SE cable or other similar cables.

    They appear to be smaller then the insulated conductors on what looks to be less then 10 AWG, but not really certain what thickness of insulation is either.

  4. #4
    Join Date
    Aug 2007
    Location
    Billings MT
    Posts
    204
    Quote Originally Posted by jap View Post
    I'd start all over.

    JAP>
    Start over in what way
    If the women dont find you handsom, at least they will fine you handy

  5. #5
    Join Date
    Jan 2007
    Posts
    3,660
    Quote Originally Posted by kenaslan View Post
    Start over in what way
    I'm picky about the control cabinets I build.

    This one just confirms how good of a job I do.


    JAP>

  6. #6
    Join Date
    Jan 2007
    Posts
    3,660
    As far as more than one conductor under a screw, it's fine on the EGC's to do that as long as the terminal is actually rated for such.


    Jap>

  7. #7
    Join Date
    Aug 2007
    Location
    Billings MT
    Posts
    204
    Quote Originally Posted by kwired View Post
    Not familiar with the cable in question, but something tells me the three together must be used as one EGC - so that sort of makes it one conductor? Kind of like the concentric bare conductor in SE cable or other similar cables.

    They appear to be smaller then the insulated conductors on what looks to be less then 10 AWG, but not really certain what thickness of insulation is either.
    Thats a 12/3 Okonite CLX 546-31-3453 with 3 #16 grounds. However if you look closely, you can see what appears to be a single #16 from the ground strip to the TB-480V ground. That wire should be up sized to a #12 and landed under its own termin.
    If the women dont find you handsom, at least they will fine you handy

  8. #8
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,031
    OT, but why is H-300X L3 (blue wire) tucked back inside the Panduit?

  9. #9
    Join Date
    Jan 2007
    Posts
    3,660
    I don't think the grounding terminal blocks on the denrail are rated for more than one conductor but I may be wrong on that.


    JAP>

  10. #10
    Join Date
    Jan 2007
    Posts
    3,660
    Quote Originally Posted by gadfly56 View Post
    OT, but why is H-300X L3 (blue wire) tucked back inside the Panduit?
    A single phase 480v load would be my guess.