    Quote Originally Posted by DrSparks View Post
    You are correct. If it is an external building fed by a feeder or a sub feeder from the main building the grounding electrode conductor would terminate on the equipment grounding bar and the neutral busbar would remain isolated from ground.
    If you were to bond the neutral to ground in the subpanel the neutral current would take parallel paths back to the service equipment possibly creating a potential difference across grounded non-current carrying surfaces
    Sent from my A574BL using Tapatalk
    I know the grounds and neutrals must be separate. What I was asking was, does the GEC have to terminate on the same terminal or bus as the EGC's? In other words could the GEC land on its own bar bolted to the enclosure, then the source and branch EGC's land on a separate bus also bolted to the enclosure.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  2. #12
    Join Date
    Jun 2014
    Madison, WI, USA
    Posts
    346
    Quote Originally Posted by electrofelon View Post
    There is nothing in the code prohibiting you from terminating the the gec on a separate terminal bar or simply a log that is bolted through the chassis as long as you insure good electrical conductivity. But why wouldn't you just terminate the GC on the ground bar?
    Tell me and I forget. Teach me and I remember. Involve me and I learn.
  3. #13
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,821
    Yes you can use the enclosure to connect the two EGC bus bars together.