    Conduit Seals in Class I, Division 1, Group B

    Back in the 'good ol days', we used to have to installconduit seals within 1.5” of the arcing device in Class I Division1 Group B environments – we therefore omitted the associated conduit union, usually a C-H UNY.
    Ican’t find any support for this in NEC. Comments?


  2. #2
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,180
    If you go back far enough and deep enough, you will most likely find it was a listing issue. [Section 110.3(B)]
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  3. #3
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    459
    Quote Originally Posted by rbalex View Post
    If you go back far enough and deep enough, you will most likely find it was a listing issue. [Section 110.3(B)]
    I would say that's correct Bob. I was just reviewing Crouse Hinds Catalog. The 1.5" requirement for sealing in Division 1, Group B is shown for 'EDS/EFS Series Control Stations' and a few other areas, in fine print.

    Thanks