Results 1 to 9 of 9
Thread: Question about bonding in a breaker panel
  1. #1
    Join Date
    Feb 2018
    Loganville, GA
    Posts
    2
    Hi I considering buying a home in Loganville, GA. and had a home inspector look at the electrical system in the home that he said it was fine. I was looking over his shoulder during the inspection and am not sure he is correct about the panel being wired correctly. I have some questions about the neutral and ground bus bar bonding at the service panel.
    Outside the home there is a 200A single phase Meter Base that has a service disconnect. From there is 4 wire feeder cable going to the service panel inside the home (separate ground and neutral and the two 120V legs). Both the ground and the neutral wires of the feeder cable are bonded together in the meter base box on the outside of the house. Inside the service panel in the house the feeder cable connections are as follows: ground wire connects to the ground buss bar and the neutral wire connects to the neutral buss bar. Also there is a #4 AWG bare copper ground wire going from the ground buss bar in the service panel to two ground rods outside the home. The ground buss bar and the neutral buss bars are bonded together in the service panel inside the home. I also noticed that the neutrals and ground wires from the individual circuits were mixed on the ground and neutral bus bars.
    So my question is, since the meter base outside has the disconnect shouldn't the ground and neutral buss bars in the service panel be separated (remove the bonding bar that runs between them), the bare #4 AWG copper wire for the ground rods be moved to the meter base where the neutral and ground feeder cables are bonded together, and the mixed neutral and ground wires in the service panel be installed on the correct buss bars? I'll have the current home owner get an electrician to make the changes if this needs corrected before I close on the home.
    Chris
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,571
    You are correct in that the neutrals and grounds should be separated at the sub panel inside the house. They should be bonded together at the service disconnect only
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Feb 2018
    Loganville, GA
    Posts
    2
    thanks
    Thanks Dennis.
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,921
    And any grounding electrode conductors need to be moved to the service disconnect or any point ahead of the service disconnect.
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,821
    Quote Originally Posted by kwired View Post
    I agree, the GEC landing in the sub-panel is incorrect.
    Rob
  6. #6
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    10,028
    I agree about the set up not being code compliant, but have a couple questions since I have seen similar set ups in the past.
    Was it ALWAYS a requirement to keep the grounds and neutrals separate in the sub panels?
    What is the real life hazard of current flowing on the ground conductor going from the disconnect to the breaker panel?
    Cheers and Stay Safe,
    Marky the Sparky
  7. #7
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,821
    Quote Originally Posted by K8MHZ View Post
    Yes. I've have yet to see documentation that states that this not required.
    Rob
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,921
    Was acceptable to use a grounded conductor only (no separate EGC) to supply separate buildings/structures.
    What is the hazard(s)?
    Potential unintended paths carrying neutral current.
    Rise in voltage (because of voltage drop on current carrying grounded conductor) over "true ground".
  9. #9
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,933
    Neutral and ground are in parallel. If the neutral was to open that would put all the neutral on the ground, potential for shock and fires, improper operation of electronic equipment, loss of 0 volt reference..
    Moderator-Washington State
    Ancora Imparo
Posting Permissions
  • You may not post replies
  • You may not edit your posts