We recently received 208 LED light fixtures from Holophane. They did not have a wiring digram with them. I asked the manufacture for one, but haven't heard from him.
Does anyone no how to terminate a 208V LED fixture that has 3-Gray wires, 3-Purple, 1-Black, 1-White and 1- Green?
black, white and green are your power.
assuming the ballast is multi volt.
what you have sounds like a lutron addressable
module. you will have two pair of those purple and gray wires
together. those will go on the eco bus. they are NOT 0-10 volt dimming leads.
the third purple and gray pair, should be separate or distinctly
different from the other purple and gray's by location or marking.
those are 0-10 volt dimmer output, to drive a standard 0-10
volt dimming ballast or dimming driver.
mixing eco bus and 0-10 volt output together will not turn out well.
i've seen half a dozen jobs recently where this has been done.
it won't kill the eco module, but nothing will dim or address. can't
be set up and programmed at all. no dimming, all the lights on the
eco system are full on, all the time.
and it seems the ones that are miswired are always in a hard lid.
lutron has their addressable modules to drive other peoples 0-10
volt stuff, and their new eco ballasts are only showing two purples
and two grays, for eco in, and eco out. no third pair.
the new eco ballasts don't look much different than the regular ballasts.
did these devices come separate from the fixtures, and look like
"spare" ballasts? i'm betting they are addressable modules, not led drivers.