Thread: pigtailing multiple EGC's in a panelboard

  1. #11
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,929
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ok, seems like the consensus is everyone does it so its kosher
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #12
    Join Date
    Jul 2003
    Location
    MA
    Posts
    2,128
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As long as the splicing connector is listed for the combination of wires spliced-compliant.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

  3. #13
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tkb View Post
    As long as the splicing connector is listed for the combination of wires spliced-compliant.
    You saying I cannot just split bolt 42 EGCs together and run only one to the ground bus?

    Yeah, prolly ain’t gonna work...
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #14
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Ok, seems like the consensus is everyone does it so its kosher

    The consensus is that it is legal for all of US to do it, we never said YOU were allowed to do it also....
    "Electricity is really just organized lightning." George Carlin


    Derek

  5. #15
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,929
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    The consensus is that it is legal for all of US to do it, we never said YOU were allowed to do it also....
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #16
    Join Date
    Feb 2007
    Location
    Alexandria, VA
    Posts
    428
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    EGC under one lug

    I often see in older panels all of the EGCs terminated under one large lug. What is the history or acceptance of this practice?

  7. #17
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Greg1707 View Post
    I often see in older panels all of the EGCs terminated under one large lug. What is the history or acceptance of this practice?
    Not legal now, wasn’t legal then. Not listed for all those small conductors.

    Some ground buses are listed for two EGC wires, but is about as good as it gets. Some weird terminals may accept three.
    "Electricity is really just organized lightning." George Carlin


    Derek

  8. #18
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,364
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Greg1707 View Post
    I often see in older panels all of the EGCs terminated under one large lug. What is the history or acceptance of this practice?
    Not legal but likely not a hazard either if they're twisted neatly and terminated in a proper sized lug.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  9. #19
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    1,892
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I use a lot of troffs above panels , make a nice 20 pos G bar w/ lug in them, elevate it above the troff 'lip ' with 1/4-20 hardware. I'll use 2 or 3 2" nipples troff to panel....There's only one (usually #4 bare cu ) running into my panels

    It's a 1/3 less messy

    ~RJ~

  10. #20
    Join Date
    May 2011
    Posts
    4,773
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    I am gonna tell you right now:

    There is absolutely no way on earth that a panelboard could be considered a raceway.......

    The enclosure/cabinet perhaps.......
    Touche. You almost had me arguing with you there.

    Quote Originally Posted by jumper View Post
    You saying I cannot just split bolt 42 EGCs together and run only one to the ground bus?

    Yeah, prolly ain’t gonna work...
    Be honest. You don't want to do that with a ground bus. You want to do it with a lay-in lug because you forgot to pick up a ground bar that morning. Or maybe you want to use just a green screw.