User Tag List
Page 1 of 3 1 2 3 LastLast
Results 1 to 10 of 27
Thread: pigtailing multiple EGC's in a panelboard
  1. #1
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,329
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    wirenutting several EGC's to a single which then goes to the ground (or neutral if service) bar. Is this compliant? I always thought it was, but looking at 250.122(C) seems to only mention raceway, cable, or cable tray. No cabinets. IS there another section I am not aware of?
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  2. #2
    Join Date
    May 2011
    Posts
    5,067
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Well, the way 250.122 (C) is written it neither prohibits or allows doing the same thing elsewhere. It simply doesn't apply to panelboards. Unless you want argue that a panelboard is a raceway. Which it arguably could be.
    A point in favor of compliance is that 312.8 allows for splices in panelboards up to reasonable limits. Also see 250.148. I guess the required size of the pigtail might be a little hard to pin down if one wanted to be particular about it.
  3. #3
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,728
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I have done it, mainly as part of residential panel upgrades. As long as the wire is at least as large as required for the largest connected circuit, you're golden.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  4. #4
    Join Date
    Jun 2004
    Posts
    5,329
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    I frequently do it too. Its hard to come up with what to cite for a violation. I cant really find anything, other than the logical progression that 250.122(C) exists therefor implying I must have permission to use a single EGC for multiple circuits, and then a cabinet or box is not listed.
  5. #5
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Legal. You cannot find a section because no section exists.
    "Electricity is really just organized lightning." George Carlin
    Derek
  6. #6
    Join Date
    Jun 2004
    Posts
    5,329
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    then they should delete 250.122(C) since it serves no purpose yes?
  7. #7
    Join Date
    Jan 2009
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    I am gonna tell you right now:
    There is absolutely no way on earth that a panelboard could be considered a raceway.......
    The enclosure/cabinet perhaps.......
    Derek
  8. #8
    Join Date
    Jan 2009
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    No, I do not think so.
    Tying the grounds together in the panel is rare. Easier to just land them usually.
    Only reason I have done it is for making room in a crowded panel.
    The section is just a clarification that favors the installer really.
    Can you imagine if we had to prove it was okay to a single ground for multiple circuits to an inspector using theory?
    Derek
  9. #9
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,980
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I agree, I have done it on some old panels where the neutral/EGC bus didn't have enough terminal holes for all of the conductors.
    Rob
  10. #10
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,736
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    At one time panels never seemed to have enough holes for both neutral and EG connections. Makers seemed to expect us to use MWBC whenever possible and spare EG bars were special order. Never, ever, did I hesitate to splice EGs. There that makes it all correct.
    Tom
    TBLO
Posting Permissions
  • You may not post replies
  • You may not edit your posts