Results 1 to 10 of 10
Thread: Mega Ohm's question
  1. #1
    Join Date
    Jun 2006
    NoDak
    Posts
    335
    Mega Ohm's question
    If you take a resistance reading with a dmm and it is set on auto, and the reading shows "M" for Mega (example, 18.42 M Ohm's), I'm assuming that would be equivalent to 18,420,00 Ohm's?
    I had a brain fart today while troubleshooting some tile floor heat, related to their rated resistance and have been second guessing myself all afternoon!
    The heating element is rated for 16 Ohm's. It's not putting out heat. No current draw at t-stat.
    Not sure if heating element was compromised during tile install. Was ohm'ing out the leads to element and definitely didn't get 16 Ohm's. Tried a couple of meters with similar results.
    After figuring this out, then need to interpret those results...
    Moderators, if you feel this belongs in different section feel free to move it...
    Thanks!
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,529
    Yes, M for Mega means that you multiply the reading by one million, 1,000,000.
    While K for Kilo means that you multiply the reading by one thousand, 1,000.
    A reading of 18Megohms is for all practical purposes an open circuit. (Although a higher voltage than is used by your DMM might break down a tiny insulating gap somewhere.)
    Note also that the presence of any residual voltage on the disconnected wires, even as little as phantom voltage in some cases, can interfere with the reading process on some DMMs.
  3. #3
    Join Date
    Mar 2016
    The Motor City, Michigan USA
    Posts
    790
    A reading of 18 MΩ is likely to be the resistance of your fingers.
  4. #4
    Join Date
    Jun 2006
    NoDak
    Posts
    335
    Yeah, I was just playing with the calculator, nameplate-> 16 Ohm's at 120v is 7.5 amps and 900 watts. What I saw-> 18.42M Ohm's is basically 0 amps and watts!
    I'm guessing the heating element got damaged...
  5. #5
    Join Date
    Dec 2012
    Posts
    19,529
    Quote Originally Posted by sw_ross View Post
    Once they develop a hot spot for any reason eventually the heater wire will burn through at that point.
    Even nichrome wire increases in resistance when it gets really hot.
  6. #6
    Join Date
    Jan 2018
    SE Michigan
    Posts
    100
    It would be wise to test the cable heating element and cold extension leads, before the floor installers show up. That way you would know who owns the problem.
    MTW
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,913
    Quote Originally Posted by drcampbell View Post
    Yes, if OP was contacting probes while testing he could have been reading through himself, always make sure you are never touching more then one probe when testing results is in meg-ohm range.
  8. #8
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,933
    I thought this was going to be the one about Mega Ohm and Milli Amp going out into an electric field and fluxing.
  9. #9
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    23,353
    Quote Originally Posted by ggunn View Post
    They rode on a Mega Cycle.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  10. #10
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,933
    Quote Originally Posted by LarryFine View Post
    At one point Milli said, "Please stop, Mega; that Hertz".
Posting Permissions
  • You may not post replies
  • You may not edit your posts