Thread: Amp meter on 2300 volts?

  1. #11
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,849
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jraef View Post
    To educate yourself more on this, watch this video. The "spider web" situation I described shows at 1:09.
    Link is missing....

  2. #12
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,224
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    To affect the current measured by either a clamp-on ammeter or a current transformer, the "shielding" would have to actually be a current carrying concentric neutral.
    Yes, that was the basis of my question. I worked a bit with MV up to 11kV but I have never seen that sort of shielding. Mostly, we use multi-core SWA but the point of measurement would be on individual conductors which are not usually shielded.
    Si hoc legere scis nimium eruditionis habes.

  3. #13
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,228
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    Link is missing....
    Added it back in. Not sure what happened there.