Thread: Amp meter on 2300 volts?

  1. #1
    Join Date
    Mar 2009
    Location
    Wilson NC
    Posts
    2

    Amp meter on 2300 volts?

    Recently the company I work for had an outside contractor install CTs on our electrical equipment. Today I was told one of the motors legs was 20 amps lower than the other 2 legs. One leg was roughly 20 amps the other 2 around 30 amps each.( this may be a faulty CT, because the motor runs fine) My question is, can I use a hand held volt meter rated for 600volts and snap the amp clamp portion on the meter around a leg at a time safely? The legs are in an over head raceway in open air. The meter is a DMM. I would not be exposed to any open cabinets to come in contact with the 2300. Thanks....Gene

  2. #2
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,600
    IMO, If you’re asking the question, I’d say your not trained.
    Tom
    TBLO

  3. #3
    Join Date
    Sep 2008
    Location
    UK
    Posts
    11,349
    Quote Originally Posted by gene6029 View Post
    Recently the company I work for had an outside contractor install CTs on our electrical equipment. Today I was told one of the motors legs was 20 amps lower than the other 2 legs. One leg was roughly 20 amps the other 2 around 30 amps each.( this may be a faulty CT, because the motor runs fine) My question is, can I use a hand held volt meter rated for 600volts and snap the amp clamp portion on the meter around a leg at a time safely? The legs are in an over head raceway in open air. The meter is a DMM. I would not be exposed to any open cabinets to come in contact with the 2300. Thanks....Gene
    I wouldn't.
    Si hoc legere scis nimium eruditionis habes.

  4. #4
    Join Date
    Jul 2006
    Location
    Roughly 5346 miles from Earls Court
    Posts
    2,587
    If you don't trust the instrumentation, schedule a shutdown and have that tested/calibrated.

    (And if the MV conductors are shielded, you won't get a good reading anyway.)

  5. #5
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,752
    ^^^Exactly

    I am surprised they didn't go any testing after installing CT's?

  6. #6
    Join Date
    Mar 2009
    Location
    Wilson NC
    Posts
    2
    Thanks guys for the info. I talked our plant manager into getting outside contractors to do the testing.

  7. #7
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,600
    Quote Originally Posted by gene6029 View Post
    Thanks guys for the info. I talked our plant manager into getting outside contractors to do the testing.
    Tom
    TBLO

  8. #8
    Join Date
    Sep 2008
    Location
    UK
    Posts
    11,349
    Quote Originally Posted by zbang View Post
    If you don't trust the instrumentation, schedule a shutdown and have that tested/calibrated.

    (And if the MV conductors are shielded, you won't get a good reading anyway.)
    What sort of shielding would there be?
    Si hoc legere scis nimium eruditionis habes.

  9. #9
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,217
    Quote Originally Posted by Besoeker View Post
    What sort of shielding would there be?
    To affect the current measured by either a clamp-on ammeter or a current transformer, the "shielding" would have to actually be a current carrying concentric neutral.

  10. #10
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    7,710
    I'm glad you heeded the advice. But just for your enlightenment:
    Quote Originally Posted by gene6029 View Post
    Recently the company I work for had an outside contractor install CTs on our electrical equipment. Today I was told one of the motors legs was 20 amps lower than the other 2 legs. One leg was roughly 20 amps the other 2 around 30 amps each.
    That's not 20A LOWER, that's 10A lower. But 10A out of 30 is a VERY SIGNIFICANT imbalance and should absolutely be investigated, so you were right to question it.

    ( this may be a faulty CT, because the motor runs fine)
    NEVER assume that meters are wrong... "Runs fine" is highly subjective. If you really have that much of an imbalance, the only thing you might notice is extreme heat showing up on an IR scanner, or total meltdown after being left running like that for too long if you didn't look for that. Side note though, one of the CTs may have the wrong ratio and the installer failed to notice. I've also seen it PRINTED WRONG on the CTs! You would think that can't happen, but I've been in a CT manufacturing facility... believe me, it's not uncommon for it to happen, but most of them get caught in the final QC (workers in most CT factories are typically illiterate 3rd world manual labor people).

    My question is, can I use a hand held volt meter rated for 600volts and snap the amp clamp portion on the meter around a leg at a time safely? The legs are in an over head raceway in open air. The meter is a DMM. I would not be exposed to any open cabinets to come in contact with the 2300. Thanks....Gene
    Those two statements are actually contradictory. Those conductors, despite being in open raceway, are STILL potentially lethal if there is any insulation leakage, it's very different from LV conductors. I've seen 2300V conductors in a dark room look like they are covered in living blue spider webs simply because (as it turned out) someone had strapped down clamps on the conductors too hard and compressed the foam core, decreasing the dielectric properties and causing a "partial discharge". Had anyone touched those conductors, they could have been killed. We couldn't see it in the light, but we could hear a "ticking" sound that turned out to be that stray voltage going jumping a 1" gap to get to ground. The sound was shrugged off by the plant manager as "normal stuff", but I knew better and had them turn off the lights. The plant manager was embarrassed to say the least. So the best practice when having to live / work around MV conductors is to ALWAYS assume they are potentially lethal.

    To educate yourself more on this, watch this video. The "spider web" situation I described shows at 1:09.
    https://www.youtube.com/watch?v=GRmOyUGAODA
    Last edited by Jraef; 02-23-18 at 05:27 PM. Reason: Re-entered link to video