Thread: Service Entrance Grounding

  1. #41
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,098
    Quote Originally Posted by Jamesco View Post
    It can't just sit there on the grounded conductor. It's looking for mother earth.



    http://www.nemasurge.org/grounding/
    Grounded conductor is connected to earth or it wouldn't be called a grounded conductor.

    But how much resistance to earth is acceptable? NEC alone doesn't really give us much for limitations other then a single ground rod has to be less then 25 ohms or be supplemented.
    I live for today, I'm just a day behind.

  2. #42
    Join Date
    Feb 2018
    Location
    Iowa
    Posts
    257
    Quote Originally Posted by kwired View Post
    Grounded conductor is connected to earth or it wouldn't be called a grounded conductor.

    But how much resistance to earth is acceptable? NEC alone doesn't really give us much for limitations other then a single ground rod has to be less then 25 ohms or be supplemented.
    What if it's 265 ohms?

  3. #43
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,098
    Quote Originally Posted by Jamesco View Post
    What if it's 265 ohms?
    If it is a single rod you have to drive a second rod to comply with NEC. Chances are it doesn't get lowered by much though. Now if you have some specification or other desire to be below a certain level - then you have some more work to do.

    And if you just drive two rods to begin with - to comply with NEC you are done, no requirement to even measure it. It could still be 265 ohms.
    I live for today, I'm just a day behind.

  4. #44
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,392
    Quote Originally Posted by Jamesco View Post
    What if it's 265 ohms?
    What do you have for a grounding electrode system at your house? You seem to think it is very important, so I assume you have something elaborate with low resistance at your house?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"