    Quote Originally Posted by jaggedben View Post
    I don't follow your logic.



    Unless there's an EV. Or two.
    I'm not that familiar with them can they run at their maximum output continuously for more than 3 hours?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #22
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,722
    Quote Originally Posted by infinity View Post
    I'm not that familiar with them can they run at their maximum output continuously for more than 3 hours?
    The tesla chargers do.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.

  3. #23
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,862
    Quote Originally Posted by ActionDave View Post
    The tesla chargers do.
    Good to know thanks.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #24
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,962
    I did say there is seldom any significant continuous loads in a dwelling.

    I don't know a lot about EV's but would think if you had a higher capacity charger, they would charge the vehicles in three hours.

    If you had a lower rate charger it may take more then three hours, but at same time that is not as significant of a load demand wise.

    Pool pumps, ERV's, boiler or hot water circulators, and such can also be continuous - but typically not too significant demand wise either.

    Besides the fact there can be some (usually not too significant) continuous loads, I don't see anywhere in art 220 where it says to apply an additional 25%. If anything there is the possibility of being able to apply demand factors in art 220.

    You do need to apply that extra 25% when selecting conductors and often the overcurrent protection for a branch circuit supplying a continuous load.