    I have a customer that is building a separate structure on his property for rental. He had an existing 200 amp service that fed his house. I did a load calculation on his house and it came out to 98 amps. What we decided to do was to replace his existing meter to a meter pack that has 2 meters and 2 main disconnects. I feed his house with a 100 amp breaker and fed the new building with 100 amps. The inspector tagged me with a code I have never seen before. He did not site a code. Has anyone ever seen this before? Am I just not seeing this in the code book?
    Attached Images Attached Images
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,298
    Quote Originally Posted by crtemp View Post
    The inspector is wrong, on two counts. The load calc already includes the 125% for any continuous loads. Besides A dwelling doesnt even have many continuous loads.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #3
    Join Date
    Jan 2013
    Wa state
    Posts
    431
    Quote Originally Posted by electrofelon View Post
    That's pretty much what I was thinking also. Just wanted to make sure I wasn't overlooking something obvious. Thanks
  4. #4
    Join Date
    Jun 2014
    Madison, WI, USA
    Posts
    326
    Definitely full of dookie. Besides what the previous poster said, I would add that it's perfectly allowed by code for the calculated connected load to be exactly 100a on a 100a service. Although it's bad design, except maybe in multi-dwelling units where there is little or no chance of future expansion.
    Sent from my A574BL using Tapatalk
    Tell me and I forget. Teach me and I remember. Involve me and I learn.
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,695
    I agree with the cartoon cat.
    I live for today, I'm just a day behind.
  6. #6
    Join Date
    Jun 2004
    Posts
    4,298
    Quote Originally Posted by kwired View Post
    https://www.youtube.com/watch?v=PkhPuH8G5Hg
    (sufferin soccotash clip)
  7. #7
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,139
    I agree also, the inspector is confused about the calculation already containing the 125% for continuous loads which in this case I would guess that none even exist.
    Rob
  8. #8
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,966
    The cartoon cat and others have made an assumption that is likely correct. But before you talk to the inspector, . . .
    . . . can you confirm that your load calculation did, in fact, include 125% for any continuous loads? If so, I agree that the inspector was in error.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  9. #9
    Join Date
    Jan 2007
    Posts
    3,524
    Quote Originally Posted by charlie b View Post
    The cartoon cat and others have made an assumption that is likely correct. But before you talk to the inspector, . . . . . . can you confirm that your load calculation did, in fact, include 125% for any continuous loads? If so, I agree that the inspector was in error.
    I was thinking the exact same thing.
    One must confirm the calculations are correct before saying the inspector was wrong, but, I agree with the others because it seems the inspector is basing his judgment solely on the 98 amps.
    JAP>
  10. #10
    Join Date
    Jun 2004
    Posts
    4,298
    Quote Originally Posted by jap View Post
    JAP>
    He is wrong on two counts. First is that the standard load calc procedure includes continuous loads. Second is that the inspector seems to think the 80% rule applies to everything.