    Hi,
    Would there be a demand factor in determining the circuit breaker size of a DC UPS panel that supplies to a switchgear (the DC panel supplies to multiple panel of the switchgear using a single circuit), given that the switchgear's CB motors, would not function simultaneously.
    Thanks for your answers,
    Ian
  2. #2
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,900
    Quote Originally Posted by lorenzian View Post
    Hi,
    Ian
    I think these would be class 1 circuits and as such there are no established requirements in the code for computing the loads. The code only has requirements for load calculations for services, feeders, and branch circuits. Class 1 circuits are not any of those. It would seem to me that would make it a design choice.