View Poll Results: Does this comply with the NEC 2014?

Voters
18. You may not vote on this poll
  • Yes.

    0 0%
  • No

    18 100.00%
Page 1 of 3 123 LastLast
Results 1 to 10 of 23

Thread: SO Cord in Residence - You Make the Call Please?

  1. #1
    Join Date
    Nov 2004
    Location
    Northern Virginia
    Posts
    1,019

    SO Cord in Residence - You Make the Call Please?

    Does the following meet the NEC 2014? If not, Code reference please. This is a connection for a residential kitchen oven.

    Thanks in advance.

    Mark

    Name:  Picture2.jpg
Views: 349
Size:  21.6 KB

  2. #2
    Join Date
    Jan 2007
    Location
    New Jersey
    Posts
    1,045
    No it does not conform.
    400.8 Uses Not Permitted. Unless specifically permitted
    in 400.7, flexible cords and cables shall not be used for the
    following:
    (1) As a substitute for the fixed wiring of a structure
    Rick Napier
    Inspector and Instructor

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,599
    Not counting the minor detail already mentioned, the strap is wrong.
    Tom
    TBLO

  4. #4
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,564
    I have no idea what that whole thing is but it is obviously DIY. Why the two pole breaker, where does the AC cable come from, why does that SO cord go to some kind of a plate on the wall and with a armored cable angle connector yet?

    -Hal

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    36,695
    Quote Originally Posted by hbiss View Post
    I have no idea what that whole thing is but it is obviously DIY. Why the two pole breaker, where does the AC cable come from, why does that SO cord go to some kind of a plate on the wall and with a armored cable angle connector yet?

    -Hal
    My guess, there was a flush box, someone thought they needed that breaker in the circuit (likely did not), extended to the breaker with the SO cord, and what you called AC is probably the FMC whip that came attached to the oven.
    I live for today, I'm just a day behind.

  6. #6
    Join Date
    Nov 2004
    Location
    Northern Virginia
    Posts
    1,019
    Quote Originally Posted by kwired View Post
    My guess, there was a flush box, someone thought they needed that breaker in the circuit (likely did not), extended to the breaker with the SO cord, and what you called AC is probably the FMC whip that came attached to the oven.
    Yes, that AC or Greenfield whip with the paint is to the oven.

  7. #7
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,973
    agree with Rick, post #2
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  8. #8
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,660
    I agree it is not to code but in the grand scheme of things as a safety hazard it is way down on the list of things I am going to worry about all that much.
    Bob

  9. #9
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,132
    Quote Originally Posted by augie47 View Post
    agree with Rick, post #2
    Me too.

    Roger
    Moderator

  10. #10
    Join Date
    Aug 2017
    Location
    Los Angeles CA
    Posts
    152
    But hey, they did use a SQ-D type QO! Above average hack