Thread: Motor troubleshooting help

  1. #11
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,978
    180307-1211 EST

    ishium 80439:

    In your first post you used the word "panel" twice, and lugs at "panel". Where is this panel? Is it the breaker panel (100 ft away from compressor) or some panel next to or on the compressor?

    If the voltages are very close to one another at the compressor, then it is clear the problem is between that point of measurement and the motor or within the motor.

    .

  2. #12
    Join Date
    Jan 2018
    Location
    SE Michigan
    Posts
    100
    I would suggest that you check the internal connections and voltages at the starter and motor. Your currents are imbalanced, and that will cause the overload to trip, even if they are lower than the overload setting value. IEC starters and electronic overload relays have differential protection built in, to protect for unbalances and single phasing.

    If you have a weak connection, it will cause the voltage to vary, and the currents will reflect the unbalanced voltages. What voltages you measure at the supply end, may not be what the motor sees.

    It could be worn starter contacts, loose or overheated connections, or bad terminations in the motor connection box. Just because the compressor service tech say's its good, doesn't make it so. Check the voltages inside the unit, at the load side of the controls and the motor.

    MTW

  3. #13
    Join Date
    Oct 2007
    Location
    Denver foothills via the Horn of Africa
    Posts
    555
    Yes, to clarify I was referring to the same panel- the one from which the compressor is fed. I first measured voltage at the main lugs and then on the load side of the breaker- these values were the same. From that breaker the wire is unbroken to lugs within the unit itself. (and for more clarity the 100' is probably closer to 80' and is the total distance including the portion of the run up the wall from the panel and back down to the compressor)
    "If you don't do it this year , you'll be one year older when you do" Warren Miller

  4. #14
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,950
    The internal thermals fail often enough. Make sure the motor is cooling. Check for dirt or crude on the cooling fins, blocked ventilation etc.
    Tom
    TBLO

  5. #15
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,900
    I like the idea of jumping out the internal OL and using an external one, at least as a test. It does not seem to me that the current levels you are seeing should trip an OL.

    You mention the internal OL is electronic. Is it possible the setting is wrong?
    Bob

  6. #16
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,900
    Quote Originally Posted by ptonsparky View Post
    The internal thermals fail often enough. Make sure the motor is cooling. Check for dirt or crude on the cooling fins, blocked ventilation etc.
    electronic overloads are not generally heat sensitive.
    Bob

  7. #17
    Join Date
    Jul 2013
    Location
    Resting under the Major Oak UK
    Posts
    1,195
    Have you carried out continuity and insulation tests on the motor windings?

    I'll be honest, it's where I would have started.
    The reports of my death are greatly exaggerated.

  8. #18
    Join Date
    Jun 2014
    Location
    Madison, WI, USA
    Posts
    346
    Quote Originally Posted by petersonra View Post
    electronic overloads are not generally heat sensitive.
    They use CTs don't they?

    Sent from my A574BL using Tapatalk
    Tell me and I forget. Teach me and I remember. Involve me and I learn.

  9. #19
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,010
    I'm with MTW on this.
    A- 29.7A, B- 23.5A, C- 18.9A
    You have a significant current imbalance, about 22%. That's going to cause most SSOL relays to trip, because a severe current imbalance will cause extra motor heating even though the current is not exceeding the setting. That's what makes SSOLs better than heater type. So DO NOT "bypass" it! It's likely doing EXACTLY what it needs to do to keep that motor from burning up!

    So the issue is, what's causing the current imbalance? Your voltage readings are showing that the current imbalance is not the result of a line voltage imbalance, so you ruled that out.

    When the IR guy said he "checked the motor", what does that mean? Megger test? If not, whatever he did was meaningless. If so, was he just checking L-G, not L-L? it could have an insulation breakdown turn-to-turn or phase to phase, but nothing going to ground. If all he did was the basic test of hooking all of the motor leads together to one megger lead and the other to ground, that would not find those other problems.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  10. #20
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,532
    Quote Originally Posted by Jraef View Post
    I'm with MTW on this.

    You have a significant current imbalance, about 22%. That's going to cause most SSOL relays to trip, because a severe current imbalance will cause extra motor heating even though the current is not exceeding the setting. That's what makes SSOLs better than heater type. So DO NOT "bypass" it! It's likely doing EXACTLY what it needs to do to keep that motor from burning up!

    So the issue is, what's causing the current imbalance? Your voltage readings are showing that the current imbalance is not the result of a line voltage imbalance, so you ruled that out.

    When the IR guy said he "checked the motor", what does that mean? Megger test? If not, whatever he did was meaningless. If so, was he just checking L-G, not L-L? it could have an insulation breakdown turn-to-turn or phase to phase, but nothing going to ground. If all he did was the basic test of hooking all of the motor leads together to one megger lead and the other to ground, that would not find those other problems.
    None of those tests would detect a shorted turn, which would greatly increase the current in one winding (therefore in two phase wires.) That seems to match the symptoms.
    An ohm measurement using AC as the applied voltage or using an impedance bridge would conclusively diagnose this problem.
    If you cannot measure one winding at a time (with delta corners being permanently bonded) you just have to realize that each measurement gives you a different series-parallel combination of all three windings.

    The amperages seen could correspond to the combination of effects of voltage imbalance and a shorted turn.

    Sent from my XT1585 using Tapatalk