    Quote Originally Posted by GoldDigger View Post
    None of those tests would detect a shorted turn, which would greatly increase the current in one winding (therefore in two phase wires.) That seems to match the symptoms.
    An ohm measurement using AC as the applied voltage or using an impedance bridge would conclusively diagnose this problem.
    If you cannot measure one winding at a time (with delta corners being permanently bonded) you just have to realize that each measurement gives you a different series-parallel combination of all three windings.

    The amperages seen could correspond to the combination of effects of voltage imbalance and a shorted turn.

    Sent from my XT1585 using Tapatalk
    What I meant to say was that the simplistic L-G megger test would not catch that, not that a L-L would... sorry, I wrote that wrong.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  2. #22
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    run it at a lower pressure
    run it at no pressue
    run it with the belts off
    measure i for all 3

    reciprocating type?
    how many pistons?

  3. #23
    Join Date
    Jan 2018
    Location
    SE Michigan
    Posts
    100
    Quote Originally Posted by Jraef View Post
    I'm with MTW on this.

    You have a significant current imbalance, about 22%. That's going to cause most SSOL relays to trip, because a severe current imbalance will cause extra motor heating even though the current is not exceeding the setting. That's what makes SSOLs better than heater type. So DO NOT "bypass" it! It's likely doing EXACTLY what it needs to do to keep that motor from burning up!

    So the issue is, what's causing the current imbalance? Your voltage readings are showing that the current imbalance is not the result of a line voltage imbalance, so you ruled that out.
    He only checked at the panel supply end, according to the OP. I wouldn't consider it ruled out just yet. I would want to see voltage readings at the load side of the starter, while loaded, before going further.

    MTW

  4. #24
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,900
    Quote Originally Posted by DrSparks View Post
    They use CTs don't they?

    Sent from my A574BL using Tapatalk
    Cts are not heat sensitive.
    Bob

  5. #25
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,900
    Quote Originally Posted by Jraef View Post
    I'm with MTW on this.

    You have a significant current imbalance, about 22%. That's going to cause most SSOL relays to trip, because a severe current imbalance will cause extra motor heating even though the current is not exceeding the setting. That's what makes SSOLs better than heater type. So DO NOT "bypass" it! It's likely doing EXACTLY what it needs to do to keep that motor from burning up!

    So the issue is, what's causing the current imbalance? Your voltage readings are showing that the current imbalance is not the result of a line voltage imbalance, so you ruled that out.

    When the IR guy said he "checked the motor", what does that mean? Megger test? If not, whatever he did was meaningless. If so, was he just checking L-G, not L-L? it could have an insulation breakdown turn-to-turn or phase to phase, but nothing going to ground. If all he did was the basic test of hooking all of the motor leads together to one megger lead and the other to ground, that would not find those other problems.
    20% is not that bad. especially when the motor is as underloaded as it is. in fact, those readings suggest to me the motor might not have been loaded at all when the readings were taken and maybe when it is loaded the readings are different.

    ETA: It appears the default setting in AB E300 electronic OL relays for current imbalance is 35% which is more than 50% higher than this situation.
    Last edited by petersonra; 03-07-18 at 04:58 PM.
    Bob

  6. #26
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,532
    Quote Originally Posted by petersonra View Post
    20% is not that bad. especially when the motor is as underloaded as it is. in fact, those readings suggest to me the motor might not have been loaded at all when the readings were taken and maybe when it is loaded the readings are different....
    A good point. I think that to a first approximation the counter-EMF will be the same for all windings, and will have its greatest effect at low slip and low power. So under those conditions a small % difference in applied voltage can make a larger % difference is effective voltage (applied voltage minus counter-EMF.)

    We might be looking for a condition that causes the OLs to trip only under certain loading conditions or only intermittently.

  7. #27
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    do you have a pic of the name plate?
    rated hp?
    rated v ?
    rated pf and eff?

  8. #28
    Join Date
    Nov 2007
    Posts
    866
    Just replace the motor and get done with it, IMO.

  9. #29
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,011
    Quote Originally Posted by Ingenieur View Post
    do you have a pic of the name plate?
    rated hp?
    rated v ?
    rated pf and eff?
    Quote Originally Posted by topgone View Post
    Just replace the motor and get done with it, IMO.
    The OP said he is already done with it, he was just looking for ideas on why it might have been tripping.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  10. #30
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,595
    Quote Originally Posted by ishium 80439 View Post
    While it was running I got readings of A- 29.7A, B- 23.5A, C- 18.9A.
    This is a severe imbalance and is NOT normal despite what anyone may tell you.

    I would have tested voltage right at the motor splices a-b, b-c, a-c. If voltage was within spec at the motor with a current imbalance like that, I would tell them to replace the motor.

    Nothing more on your part needs to be done at this point, no OL's need to be bypassed, etc. They just need to replace the motor. That's the first step.