    Quote Originally Posted by DrSparks View Post
    When you enter gray areas like that you should err on the side of caution. Being an engineer I'm sure you know that a human body's impedance to ground is less when standing on a slab on grade

    Sent from my A574BL using Tapatalk
    What if there is a vapor retarder and/or insulation under the slab?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #22
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2017
    Posts
    4,976
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jap View Post
    What code section would require that?

    Jap>

    Let's try within 6' of a sink for starters.
    If you aim at nothing, you will hit it every time!

  3. #23
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,488
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jap View Post
    What code section would require that?

    Jap>
    210-8 (B) 5-6

  4. #24
    Join Date
    Jan 2007
    Posts
    3,821
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    Let's try within 6' of a sink for starters.
    A sink was never mentioned in the original post.

    Just dog grooming area.

    JAP>

  5. #25
    Join Date
    Jan 2007
    Posts
    3,821
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Buck Parrish View Post
    210-8 (B) 5-6
    That's the one I was looking for.

    Thanks.

    JAP>

  6. #26
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,359
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jap View Post
    A sink was never mentioned in the original post.

    Just dog grooming area.

    JAP>
    I didn't see a sink mentioned either and even if there was one a receptacle could be more than 6' away without GFCI protection.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #27
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,818
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Andy Delle View Post
    Sorry, didn't mean to sound defensive. But dare you ask any form of a DIY question over on HVAC talk and you get your butt chewed!
    DIY advice isn't permitted here either.

    Determining what is DIY advice and what is just technical information is sometimes a bit of a fine line.

    Some comments on various replies:

    10 x 13 addition was mentioned. This is large enough to be used for many different things. What is is called on any permits, zoning documents, etc?

    Is there drains in the floor and is used as or has a washdown area?



    From 210.8(A)(2):"Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use"

    Seems most would call this an area covered by this section.

    If it is determined to be a habitable area then it likely needs to have receptacles in compliance with 210.52 and possibly even AFCI protection.
    I live for today, I'm just a day behind.

  8. #28
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,488
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I didn't see a sink mentioned either and even if there was one a receptacle could be more than 6' away without GFCI protection.



    You really need to wash that dog before you groom it. Mine got sprayed by a skunk. Some one said pour tomato juice all over him. Wow, I don't recommend that. With that long hair he was a bloody mess, for sure then.

  9. #29
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,818
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    OP did mention this is not for a dog grooming business - so apparently just for the owner's own dog grooming purposes. May or may not have bare concrete floor and washing area, or even could just have a tub or shower space that is for washing.

    If there is a basin and a tub or shower then it fits the NEC definition of bathroom.
    I live for today, I'm just a day behind.

  10. #30
    Join Date
    Jan 2007
    Posts
    3,821
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Buck Parrish View Post
    You really need to wash that dog before you groom it.
    Nahh,,,, they just charge extra for that.

    As far as a GFI Receptacle being required going by the original post that "Indoor Wet Location" would seem to be as close as we can get to requiring one.

    But some would even argue that including myself.

    All the talk about sinks, power washing the floor, washing the dog prior to grroming,etc... is all speculation.

    Going strictly by the facts of the original post, I would say GFI is not required.

    JAP>