Page 3 of 4 FirstFirst 1234 LastLast
Results 21 to 30 of 36
Thread: What are the most common mistakes?
  1. #21
    Join Date
    Oct 2017
    多伦多
    Posts
    28
    Quote Originally Posted by nickelec View Post
    How about the most common thing inspectors fail you for when you know it's right but the inspector is not to smart
    Sent from my SM-G950U using Tapatalk
    Agreed
    从我的 iPhone 发送,使用 Tapatalk
  2. #22
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,432
    Quote Originally Posted by cowboyjwc View Post
    Because they are looking at it like the PV system is feeding to the panel (like it's usually drawn). Being an electrician I always plan check it backwards from the service to the panels. I just heard someone say that an inspector made him change it the other day, in another jurisdiction of course.
    Oh, I get why an inspector might look at it that way, but of course it is wrong. You'd think that all they would have to do to see it is to realize the the blades and fuses would be hot when the switch is open. I can't find anything in the NEC that explicitly says this, but it should be as obvious as not sticking your finger into a live light socket. That's not in the code, either.
    One thing that should be obvious is that the OCPD in a PV inverter output circuit is to protect the conductors from fault current coming from the service; an inverter is a current limited device and if a system is designed correctly the inverter is incapable of endangering the conductors. In the event of a fault in the inverter circuit, the direction of the current flow is reversed from normal operation, going through the switch from line to load. That should make the inspector happy.
    But you know all that, right?
  3. #23
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    There is a list of the 10 most common violations of Virginia electrical code somewhere on the internet, however the most common violations I see are as follows:
    In no particular order, flying splices (no j-box), improperly secured Romex, box fill blown (overloaded ), three prong receptacles used on 2-wire circuits, incorrect panel schedules, too shallow burial depth for conduit, poorly made connections, improper wall or Firestop penetrations, boxes set too far back in the wall, wires too short in the box, improper grounding, comcables strapped to everything they should not be like other conduit sprinkler pipe laying on the grid, etcetera.
  4. #24
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,758
    Quote Originally Posted by RICK NAPIER View Post
    I give an 8 hour seminar on this topic.
    We have to pay before we hear any specific answers from you?
    Quote Originally Posted by Coppersmith View Post
    Not charging enough for your services.
    I live for today, I'm just a day behind.
  5. #25
    Join Date
    Apr 2006
    Simi Valley, CA
    Posts
    8,333
    Quote Originally Posted by ggunn View Post
    I only inspect about 5 PV systems a day on average.
    I can build anything you want if you draw a picture of it on the back of a big enough check.
    There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.
    John Childress
    Electrical Inspector
    IAEI / CEI / C10
    Certified Electrical Inspector
  6. #26
    Join Date
    Jan 2007
    New Jersey
    Posts
    1,045
    Quote Originally Posted by kwired View Post
    No just have to many examples to list but here's a couple.
    250.24 A (4) The Grounding Electrode Conductor must bond either directly to the neutral or to the grounding bar only if it is connected to the neutral bar with a main bonding jumper. This is a problem at outdoor mains.
    314.27 Lighting outlet boxes shall be able to support 50 lbs. Exceptions for wall boxes if marked with weight limit or the fixture is less than 6 lbs. And when they use the right box it's often mounted with sheet rock screws.
    Rick Napier
    Inspector and Instructor
  7. #27
    Join Date
    Feb 2013
    Mississippi
    Posts
    341
    Name:  EGC Connection.jpg
    Very common around here EGC twisted and one left long
  8. #28
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by DBoone View Post
    I don't know of any inspector that would pass that around here without the grounds tied together either with a Buchanan, wago, or a wire nut.
    you're kidding about the one wire being left long part right?
  9. #29
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,607
    Quote Originally Posted by JFletcher View Post
    I don't think he is kidding. I think he is talking about leaving one of the EGC long to use as the pigtail to the device.
    If you aim at nothing, you will hit it every time!
  10. #30
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,835
    Incomplete for rough-in inspection, otherwise no problem except for the left-handed twist.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
Posting Permissions
  • You may not post replies
  • You may not edit your posts