    Mislabeled submersible pump?

    I recently installed a VFD for a 20HP submersible pump used for irrigation.

    The customer added a backup 20HP pump last week, so we installed a double-throw switch ahead of the VFD to connect both.

    The new pump is causing an overload shutdown on the drive.

    Existing 20HP pump pulls 55A. The new pump pulls 66A. The box clearly says it’s a 20HP pump, and per the manufacture chart should pull 54.3A.

    Could the FLA vary that much, or is it likely mislabeled?

    Per the same chart the 25HP has an FLA of 65A. Just by the numbers I think they installed a 25HP.


    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr.

  2. #2
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,233
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by brantmacga View Post
    I recently installed a VFD for a 20HP submersible pump used for irrigation.

    The customer added a backup 20HP pump last week, so we installed a double-throw switch ahead of the VFD to connect both.

    The new pump is causing an overload shutdown on the drive.

    Existing 20HP pump pulls 55A. The new pump pulls 66A. The box clearly says it’s a 20HP pump, and per the manufacture chart should pull 54.3A.

    Could the FLA vary that much, or is it likely mislabeled?

    Per the same chart the 25HP has an FLA of 65A. Just by the numbers I think they installed a 25HP.


    Sent from my iPhone using Tapatalk
    Just a thought are the motors physically the same size?
    Si hoc legere scis nimium eruditionis habes.

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,296
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A double throw switch ahead of the VFD to connect both?
    Tom
    TBLO

  4. #4
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,233
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    A double throw switch ahead of the VFD to connect both?
    I assumed either rather than both.
    Si hoc legere scis nimium eruditionis habes.

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,813
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Do you have same flow rate, pressure and amount of lift for both pumps? Vary any of those and the motor shaft sees a different load. Difference in pump speed or impeller design can change flow or pressure when everything else is the same.

    ADD:

    In fact a restriction in one output line that goes unnoticed will lessen flow and will have lesser load on that pump with everything else being the same.
    I live for today, I'm just a day behind.

  6. #6
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,296
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Submersibles often run into SFA. Is the pump running open discharge? Worst case scenario esp if it happens be a bit further down the hole.
    Tom
    TBLO

  7. #7
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    4,273
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Submersibles often run into SFA. Is the pump running open discharge? Worst case scenario esp if it happens be a bit further down the hole.
    It is ... they haven’t plumbed it into existing system yet. But so was the existing motor when I installed the Vfd.


    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr.

  8. #8
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    1,911
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the pump has a bad bearing or anything else that slows it down, the amp draw will rise.

  9. #9
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    904
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    ... if it happens be a bit further down the hole.
    The depth of the water, not the depth of the pump, determines the pressure difference across the pump.
    (along with other factors that are presumably constant)

  10. #10
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,296
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by drcampbell View Post
    The depth of the water, not the depth of the pump, determines the pressure difference across the pump.
    (along with other factors that are presumably constant)
    yes, I misspoke.
    Tom
    TBLO