    Gents,
    For a three-phase protection current transformer, is it OK to jumper together polarity marked leads to create a Y and bring out non-polarity conductors to a protective relay? I recently saw a configuration depicted in the attached sketch where the CT upstream of protected equipment had the polarities connected together, which threw me off, since the CT has to be properly installed & wired in the field to function properly in a scheme.
    Please provide your insight. The CT configuration on the left is what I'm used to seeing ..
    Thanks,
    FaradayFF
    Attached Images Attached Images
  2. #2
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    the pdf is blank
  3. #3
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,145
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ingenieur View Post
    the pdf is blank
    It displays fine in the Preview application on a Mac and in the Drive PDF viewer and the Acrobat app on my Android phone.
    Did you download the attachment instead of just expecting the diagram to show up in the browser?
  4. #4
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,568
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I can read the pdf and, to answer the OP, it will depend on whether the "protected equipment" induces a phase-shift AND whether the "microprocessor based relay" can be programmed to recognize the phase-shift, if any, along with the CT wiring configuration. Many modern relays would have no problem.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.
  5. #5
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    just tapped it
    all other pdf's just pop open
    iphone 6
  6. #6
    Join Date
    Dec 2012
    Posts
    20,145
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    just tapped it
    iphone 6
    Possibly a non-Adobe PDF that does not play well with iPhone viewer? Try downloading and opening with Adobe app.
  7. #7
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    very common
    http://www.gegridsolutions.com/multi...tsci/art07.pdf
    still can't see the pdf
    we do it all the time and the common residual/gf
  8. #8
    Join Date
    Feb 2016
    Illinois
    Posts
    1,339
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Displayed fine on my iPhone 7.
  9. #9
    Join Date
    Nov 2016
    Honesdale, PA USA
    Posts
    70
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Common depending on application...
    Quote Originally Posted by FaradayFF View Post
    Gents,
    Thanks,
    FaradayFF
    Your pdf file shows the supply CT wired 180° different from the load side CTs. This is common for some differential relay applications. You did not indicated the make and model of the relay. Note that the operating coils in the relay are also 180° from each other and this may be the reason the load CTs are wired with opposite polarity. I would need the make and model of the relay used and it would be helpful to know that device is being protected.
  10. #10
    Join Date
    Jan 2018
    California
    Posts
    22
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The CT is part of a differential scheme protection delta(L)-Y grounded(H) Transformer. The relays are Schweitzer relays. I'm thinking that unless the relay is programmed to account for the reverse polarity connection of the load site CT, it may mis operate.